Results 14 to 26 of 32
    ottawa canada
    every time temp or pressure sensor is found faulty and replaced, need to rebind? only on ucp2 and 530??
    Yeah but when you do UCP2 you need an east/west pole magnetic screwdriver
    Nov 2010
    Somewhere in the Rockies
    On ucp2, no binding. On CH530 you'll always have to bind in the new device.
    A land down under
    So does that mean the east/west pole magnetic screwdriver I went out and bought for UCP2 work was a waste of time - I'm going back Monday and demanding a refund
    ottawa canada
    They sucked you in too ???? Dont forget to take the Tartan paint back as well !!!!!
    And ask for the long stand while your at the counter .
    Apr 2011
    White Sands Missile Range, New Mexico
    having problem with trane rtac 200 ton ,hex code 5fd comm loss:suction pressure cprsr 2a ,this occured after lightning storm. is this most likely a sensor. getting stupid as i get older, what is MP and funtional ID
    A land down under
    Quote Originally Posted by socorrobob View Post
    Comm loss could be an issue with either your transducer or the comms wiring/connectors. You need to connect with TechView software to diagnose correctly.
    MP is the CH530 microprocessor, all the CH530 LLIDS (Low Level Inteligent Devices)/sensors, transducers, I/O boards, EXV,s etc connect to the MP via a comms bus. Functional ID and node number is assigned to the devices during binding (TechView process for connection to the comms bus). Functional ID is identification of the LLID, e.g Suction Pressure Transducer CPSR 2A.
    The attached link to Trane.com will provide some reading for a better explanation and guidance on troubleshooting
    http://www.trane.com/Commercial/Uplo...a-en-final.pdf
    Apr 2011
    trane rtac comm problems
    Sure appreciate help fella's.Awaiting my TechView software.after resetting this alarm it will function for about 10 minutes. Big Thankyou to "Screwit"for advice and resource info. socorrobob
    The Hot South
    You shouldn't have to "await" TechView software as it's a free download at Trane.com.
    http://www.trane.com/COMMERCIAL/Desi...ew.aspx?i=1435
    You can download the software, buy a standard 9 pin male X female serial cable, and read the bulletin that screwit posted.
    Apr 2011
    Thanks "R123" will download info and get out to this chiller in the am.
    Nov 2011
    please tell me
    south pole magnetic screwdriver this is special made by trane or we can use any piece of south pole magnetic for slecting the device .
    The Hot South
    You can use any south pole magnet. You can use any screwdriver with a magnet on the back and if it's in backwards, yank it out with pliers and put it in the other way.
    Not in Iran
    Good thread
    no signature blast'em man blast'em
    !!!KILL THE TERRORIST!!!
    Apr 2011
    yes Trane does sell a pocket size south pole magnet, happy holidays.