Results 1 to 13 of 35
08-14-2010, 11:17 PM #1
What determines the static pressure?
or standing/still state/equalized refrigerant loop pressure of a stopped system.
If the entire system is at uniform temperature, it will be whatever the unit is at, so if you leave a window A/C in your trunk and its at 120F, the entire hermetic system will pressurize to 264 psi or so for HCFC-22
In the case of a split system where the condensing unit's sun baked to 120F and evaporator coil is at 90F, what can I expect the static pressure to be?
Lowest temperature point, highest point, or something in between?
For a package RTU in Phoenix, AZ on a 105F baked in the sun, is it unreasonable to assume it will reach 135F? (vapor pressure of R-22 is 315 psi).
This means you can leak test any component using nitrogen at whatever R-22 vapor pressure system is expected to see under normal design parameters, no? So for a RTU package, even if you don't know the maximum permissible pressure, its ok to pressurize the system to at least 315 psi, no?
08-14-2010, 11:36 PM #2
Is this a drunken post? lol
08-14-2010, 11:39 PM #3
Banned
- Oct 2003
- Washington
- 7,405
Let me answer your question:
08-15-2010, 01:26 AM #4
- Jul 2010
- 25
I wonder if the OP is the same guy that owns this pickup.
http://hvac-talk.com/vbb/showthread.php?t=609492
08-15-2010, 02:02 AM #5
Measure the pressure when the system isn't running.....? Just kidding...here you go:
08-15-2010, 03:19 AM #6
HERE'S YOUR SIGN!!!(Jeff Foxworthy)
08-15-2010, 05:43 AM #7
- Sep 2007
- Newark, Ohio
- 110
08-15-2010, 06:12 AM #8
I thought it was a good question.
The static pressure will be at or close to your outdoor temp(accuracy of gauges?). Since there will still be some liquid refrigerant in the condenser.
08-15-2010, 09:07 AM #9
Wouldn't that be standing pressure?
2 Tim 3:16-17
RSES Certificate Member
AOP Forum Rules:
08-15-2010, 10:05 AM #10
never thought of hooking up my manometer
08-15-2010, 12:41 PM #11
08-15-2010, 12:46 PM #12
- Jul 2010
- middle tn
- 21
i agree with been. but what are you trying to determine with that measurement?
08-15-2010, 01:18 PM #13
Ima smartazz