    Problems with XCI Controls/EcoJay Res. zone controls?

    Anyone using these controls have problems with zone board failures after thunderstorms? Model#s: SZ-2D, SZ-4D.

  2. #2
    This is typically caused by power surges. This 24V board cannot handle more than 30V without causing failure or problems. I highly recommend that you install a line voltage surge protector at wherever you have installed your transformer and install one on the 24V connection. You can not have too much surge protection.

  3. #3
    Join Date
    Aug 2010
    Location
    Winston-Salem, NC
    Posts
    12
    Got word on this issue from manfacturer that the "wiring" on the board was incorrect. The thunderstorms were just coincidental. This issue has been resolved by the manufacturer.