Problems with XCI Controls/EcoJay Res. zone controls?
Anyone using these controls have problems with zone board failures after thunderstorms? Model#s: SZ-2D, SZ-4D.
-
04-04-2011, 11:10 AM #2
New Guest
- Join Date
- Apr 2011
- Posts
- 2
This is typically caused by power surges. This 24V board cannot handle more than 30V without causing failure or problems. I highly recommend that you install a line voltage surge protector at wherever you have installed your transformer and install one on the 24V connection. You can not have too much surge protection.
-
04-20-2011, 09:01 PM #3
Regular Guest
- Join Date
- Aug 2010
- Location
- Winston-Salem, NC
- Posts
- 12
Got word on this issue from manfacturer that the "wiring" on the board was incorrect. The thunderstorms were just coincidental. This issue has been resolved by the manufacturer.