    Have a Hussman model HLA-30-MT with a com-trol 4000 and in the summer I get a alarm that says open sensor and its says " sy-2-lig " Question where is the sensor and how can I check it, there is 40% in the tank and it only does it it the summer months not in the winter only when the outside is above some where above 80. thank you for your help, have a great day.

  2. #2
    Join Date
    Aug 2002
    Posts
    6,047
    Post Likes
    Condensate Dave probably knows this one better than I.
    But oh well .... he's not home yet.

    If it's only alarming during hotter months, possibly it's under charged. Could the sensor be near the condensor?
    There is a ohm value for that sensor at a given level. If the factory can provide you with that value, then you can simply ohm it out when it gives you the alarm.
    And to do this would not require finding the sensor. Just make a phone call.


    Or ... you can do what DiceMan did one time ... bypass the sensor with foil tape.

  3. #3
    Join Date
    Feb 2003
    Posts
    1,172
    Post Likes
    That sensor is possibly on the condensor drop leg line and is exceeding its temp. ratings. when the return temp rises
    To find it
    Go To
    Main Menu
    Tasks settings
    Analog ins
    Find Highlight the "sy-2-lig" and hit Enter
    This should show its boardpoint find it and trace out the wiring.
    There are 2 temp ranges for those sensors, it could be the wrong range.




    Watts New, Ohm My, I been Electrically Commutated. Are U2.

  4. #4
    Join Date
    Sep 2001
    Location
    East Stroudsburg, PA
    Posts
    13,215
    Post Likes
    McCoolio is most likely correct.

    Probably a low temp sensor where a high temp is supposed to be.

    I would interpret that "sy-2-liq" to mean "system #2 Liquid". Are there sensors on each liquid line????? That's unusual. Most likely a dropleg temp sensor, to bring in a recevier bypass valve...

    Does the head go nuts at any time???

  5. #5
    Join Date
    Oct 2004
    Posts
    4
    Post Likes

    thank you all

    sy-2-lig I think means rack # 2 Liquid. there are 3 racks with four copeland compressors on each. I will check out the dropleg thank you all and have a great day bob

  6. #6
    Join Date
    Sep 2004
    Location
    cyberspace, FL.
    Posts
    226
    Post Likes
    That was good info, thanks! Never knew a rack till this past july....... I like 'em.
    Teach the Gospel daily and if necessary use words.

  7. #7
    Join Date
    Aug 2002
    Posts
    6,047
    Post Likes
    Originally posted by jappell
    That was good info, thanks! Never knew a rack till this past july....... I like 'em.

    Racks are neat! It's jus the OIL THAT STINKS!!!

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.