    What determines the static pressure?

    or standing/still state/equalized refrigerant loop pressure of a stopped system.

    If the entire system is at uniform temperature, it will be whatever the unit is at, so if you leave a window A/C in your trunk and its at 120F, the entire hermetic system will pressurize to 264 psi or so for HCFC-22

    In the case of a split system where the condensing unit's sun baked to 120F and evaporator coil is at 90F, what can I expect the static pressure to be?

    Lowest temperature point, highest point, or something in between?

    For a package RTU in Phoenix, AZ on a 105F baked in the sun, is it unreasonable to assume it will reach 135F? (vapor pressure of R-22 is 315 psi).

    This means you can leak test any component using nitrogen at whatever R-22 vapor pressure system is expected to see under normal design parameters, no? So for a RTU package, even if you don't know the maximum permissible pressure, its ok to pressurize the system to at least 315 psi, no?

  2. #2
    Join Date
    Mar 2007
    Location
    State of Confusion
    Posts
    1,210
    Is this a drunken post? lol

  3. #3
    Join Date
    Oct 2003
    Location
    Washington
    Posts
    7,405
    Let me answer your question:


    http://www.youtube.com/watch?v=35Lt4bIXyrY

  4. #4
    Join Date
    Jul 2010
    Posts
    25
    I wonder if the OP is the same guy that owns this pickup.
    http://hvac-talk.com/vbb/showthread.php?t=609492

  5. #5
    Join Date
    Apr 2007
    Location
    Saint Augustine, Florida, United States
    Posts
    1,155
    Measure the pressure when the system isn't running.....? Just kidding...here you go: http://www.youtube.com/watch?v=YkCXg...x=0&playnext=1

  6. #6
    Join Date
    May 2010
    Posts
    232

    Talking

    HERE'S YOUR SIGN!!!(Jeff Foxworthy)

  7. #7
    Join Date
    Sep 2007
    Location
    Newark, Ohio
    Posts
    112
    Quote Originally Posted by ICanHas View Post
    If the entire system is at uniform temperature, it will be whatever the unit is at, so if you leave a window A/C in your trunk and its at 120F, it's around 264 psi for HCFC-22


    In the case of a split system where the condensing unit's sun baked to 120F and evaporator coil is at 90F, what can I expect the static pressure to be?

    Lowest temperature point, highest point, or something in between?
    If your trying to determine the type of refrigerant in the system (or air in system) what is wrong with that question? I would like the answer also.
    He is referring to the static pressure of the refrigerant not the static pressure of the air.

  8. #8
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,125
    I thought it was a good question.

    The static pressure will be at or close to your outdoor temp(accuracy of gauges?). Since there will still be some liquid refrigerant in the condenser.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  9. #9
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    18,593
    Wouldn't that be standing pressure?
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist

    AOP Forum Rules:







  10. #10
    Join Date
    Jan 2009
    Location
    Indiana
    Posts
    3,228
    never thought of hooking up my manometer

  11. #11
    Join Date
    Aug 2010
    Posts
    2,839
    Quote Originally Posted by timebuilder View Post
    Wouldn't that be standing pressure?
    Oops... I may have missed a word, but when was talking about R-22 and pressure in psi instead of air in inches water, I'm sure you gys figured out what I meant.

  12. #12
    Join Date
    Jul 2010
    Location
    middle tn
    Posts
    21
    i agree with been. but what are you trying to determine with that measurement?

  13. #13
    Join Date
    Apr 2007
    Location
    Saint Augustine, Florida, United States
    Posts
    1,155
    Ima smartazz

Page 1 of 3 123 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event