Results 1 to 2 of 2
  1. #1
    Join Date
    Jul 2010
    Location
    Cambridge, MA
    Posts
    14
    Post Likes

    Question about boiler size

    I know there are many other factors, but I'm wondering if 80K BTU boiler is sufficient to heat about 65 Ft of baseboard? I'm in the Northeast (1400sf reasonably insulated home) I figure 66-70 degrees for indoor wintertime temp. I can go up to 105KBTU, but I don't want to oversize if its not necessary.

    I'm sure there's lots more information that's needed to make a specific recommendation, but I'm just curious if 80K is theoretically big enough.

    Thanks.

  2. #2
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    38,475
    Post Likes
    Do a heat loss calc to do it right.

    Typical 3/4" fintube is about 600 btu a feet (at 180°) so that would mean you need an I=B=R of 39K. Much more and she'll sit on limit which can cause condensation in the flue and higher gas bills.