Question about boiler size
I know there are many other factors, but I'm wondering if 80K BTU boiler is sufficient to heat about 65 Ft of baseboard? I'm in the Northeast (1400sf reasonably insulated home) I figure 66-70 degrees for indoor wintertime temp. I can go up to 105KBTU, but I don't want to oversize if its not necessary.
I'm sure there's lots more information that's needed to make a specific recommendation, but I'm just curious if 80K is theoretically big enough.
Thanks.
-
08-13-2010, 01:54 PM #2
Do a heat loss calc to do it right.
Typical 3/4" fintube is about 600 btu a feet (at 180°) so that would mean you need an I=B=R of 39K. Much more and she'll sit on limit which can cause condensation in the flue and higher gas bills.