ADP Coil Number
Hello
Went on a service call, found this coild ADP model# HA02230A130A000067 serial# 6907L14482 what is the SEER of this coil ? and Is this coil from 1997 thanks for your help
-
08-11-2010, 11:34 PM #2
Regular Guest
- Join Date
- Jul 2010
- Location
- DFW -> Texas
- Posts
- 446
Sure looks like a 10 seer to me.
2.5 ton 13" wide 12" tall coil. Come with a .65 piston.
-
08-11-2010, 11:39 PM #3
Regular Guest
- Join Date
- Feb 2006
- Posts
- 33
thank you Joker. I went out tonight on a service call. A company replaced the Condenser last year with a Carrier 13 SEER R22 unit. Left this ADP Acoil in. They have had excessive sweat going on the furnace , SUperheat is dead on, Airflow good, Drain clear. Prolly the coil cant keep up.
-
08-11-2010, 11:48 PM #4
Regular Guest
- Join Date
- Jul 2010
- Location
- DFW -> Texas
- Posts
- 446
-
08-11-2010, 11:50 PM #5
Regular Guest
- Join Date
- Feb 2006
- Posts
- 33
they said the AC runs for half an hour, well if its hot as hell outside it will run longer. Sometimes it never gets to 71* in the house
-
08-11-2010, 11:53 PM #6
Regular Guest
- Join Date
- Feb 2006
- Posts
- 33
what would be some symptoms of a mismatched coil? I see ALot of sweat ( due to 60wb indoor) on the cap tubes after the orifice and through the manifold on the suction line for the Acoil.
-
08-12-2010, 12:04 AM #7
Regular Guest
- Join Date
- Jul 2010
- Location
- DFW -> Texas
- Posts
- 446
Sounds normal to me. May I do not understand.
It should start sweating after the piston(or metering device.)
If water is dropping down on the furnace from the inside then most likely a pan problem if the coil is someone knew. If the water is sweating on the outer cover and going down the side of the furnace then its an insulation problem.
-
08-12-2010, 12:18 AM #8
Regular Guest
- Join Date
- Feb 2006
- Posts
- 33
understood. Its not on the outside,its on the inside. Another thing I noticed is that the Acoil is installed maybe a couple inches from the top of the plenum. Can Air flow be bouncing and blowing condensate off the coil? Condenser replaced last year and This year is hotter and they are having problems now.
-
08-12-2010, 12:48 AM #9
Regular Guest
- Join Date
- Jul 2010
- Location
- DFW -> Texas
- Posts
- 446
If the coil is good then not likely. Now some coils that have been chemically cleaned alot can lose their 'slickness' and water can drop off before it rolls into the pan. Damaged fins on the coil can also cause problems.
Where exact is the water coming from?
Are we talking down the middle of the furnace or up front where the gas valve is?
I assume this is in a closet or up flow.
-
08-12-2010, 07:32 AM #10
Regular Guest
- Join Date
- Feb 2006
- Posts
- 33
it looks like its coming from the sides. But where the T or manifold on the Coil has alot of sweat from what it looks like to me. Regardless if the pan is cracked or not im prolly better off replacing the A coil due to SEER mis match and maybe the pan is cracked.