    CCOntrols BASRT-B Router

    Any one ever used sitebuilder to set up a Bacnet/IP
    from the comp to a BASRT-B Bacnet/IP to MSTP router
    BQT can see the mstp device fine, but modtest inside sitebuilder
    does not see even the router.

  2. #2
    Join Date
    Dec 2006
    Location
    What? Who? Where?
    Posts
    2,220
    Post Likes
    If you mean modstat, this is a proprietary ALC function. Other BACnet devices do not support this function. I have used both the BASRT-B and BASRTP-B with success on ALC controllers using MSTP.

    kontrol out
    "Good" - Jocko
    "Open is as open does." - Forrest Gump
    "Can't we all just get a Lon?" - Garry Jack
    "BACnet: integration or interrogation?" - The Janitor
    "Open protocols? You can't handle open protocols!" - Nathan R. Jessup
    “What’s that? Aaa… open protocols? Don’t talk about…. open protocols? Are you kidding me? Open protocols? I just hope we can hardwire an interface!” - Jim Mora Watch it here!