    Just a simple question here. Does adding a supply normally reduce overall static pressure readings? Just curious.
    George
    In a machine room
    simple answer; yes
    Massachusetts
    George, that's not such a simple question. Let me illustrate. Let's suppose you've aready got sufficient return air to have a -.02 RA static. But the air filter is plugged solid so the RA statis is now -.08. Adding another return won't change that reading at all because the problem isn't lack of RA outlest, it's another problem in the system. Adding another return to an undersized duct for example, won't change the static. Adding 10 more returns with huge ducts won't change the total static if the supply side is undersized and/or restricted. So you see, it's not just a "yes" or "no" answer. Static is really the 'bood pressure' of the system and just like in the body, the entire distribution system is part of the problem and all of the solution.
    In a machine room
    He asked a simple Q about the supply side and yes more outlets means less supply static.