The heat pump's ductwork is in the attic - taped, and insulated (no large leaks). The HRV/ERV setup is one of dedicated return in common area (this 6" rigid return is run in conditioned space only) , and HRV/ERV fresh supply tied to the Fan Coils (Bryant FE4) main supply trunk.
1)With this type of set up would the fancoil blower need to
be running ?
2)What is the major problem with running a fan coil blower
continous low ?,
3)I read on the "Puretech" thread that running the blower
on continous causes mold ? how ?
Thanks,
Nick
-
09-12-2004, 08:34 PM #2No problem operating the fan continously during the non-cooling season. Operating the fan during the a/c operation re-evaporates any moisture on the a/c coil at the end of the cooling cycle. This is 4-7 lbs. of moisture per off cycle. The evaporation elevates the indoor humidity as it dries the coil and ducts. As the indoor humidity levels rises, the a/c removes more moisture. The net effect is a a more humid house with drier coil/ducts. All things considered, do not operate the fan continously if the indoor humidity is +50%RH.Originally posted by nicholasa
The heat pump's ductwork is in the attic - taped, and insulated (no large leaks). The HRV/ERV setup is one of dedicated return in common area (this 6" rigid return is run in conditioned space only) , and HRV/ERV fresh supply tied to the Fan Coils (Bryant FE4) main supply trunk.
1)With this type of set up would the fancoil blower need to
be running ?
2)What is the major problem with running a fan coil blower
continous low ?,
3)I read on the "Puretech" thread that running the blower
on continous causes mold ? how ?
Thanks,
Nick
-
09-13-2004, 01:22 AM #3
Professional Member*
- Join Date
- Jul 2001
- Location
- Central MN and the Twin Cities
- Posts
- 1,516
Her we have to interlock our HRV's with the blower motors so that the HRV turns on the blower when it runs. If the air exchanger is tied into the main ductwork then you want the furnace/airhandler blower running with the HRV. If you do not want it to run all the time then get them to "interlock" them. They make kits for this.
Warning: Just because I am over the head injury doesn't mean I'm normal!
The day I stop learning.... I'm dead!
-
09-14-2004, 07:34 AM #4
Regular Guest
- Join Date
- May 2004
- Posts
- 58
Grasshopper,
how are You ducting the your HRV's ?
If both the fresh air and stale air is plumbed into the main trunk (of the Air handler), then yes the air handler's fan must run for the HRV to work.
In this case there is a dedicated return for the HRV, and the fresh air supply will be tied to the Air handler's supply trunk. Without interlocking the air handler's fan, would the fresh air cycle out the supply closest to the HRV return ?
Nick
-
09-21-2004, 12:49 AM #5
Professional Member*
- Join Date
- Jul 2001
- Location
- Central MN and the Twin Cities
- Posts
- 1,516
Nick- here in our state they require that anytime the HRV and the furnace share ductwork that the two be interlocked. I would suspect that it is in part to that the fan on the HRV only moves a fraction of the air that the furnace does and will not apply the proper preasure on the ductwork to deliver it. We duct our HRV's depending on the job. In new construction we often have seperate duct system just for the HRV. In retro fit we go into the existing ductwork.