    Walk-in freezer, won't pull below 4

    Hello

    First post , tho I read as a guest.

    Like to run this problem past other techs, I must be missing something.

    New customer, about 6 mths, no work on this unit till last week

    Walk-in freezer 10x10 system approx 6 years old

    2 fan Evap facing door

    Cond on roof, 38' run with 10' being vertical,trapped at evap.

    Cond has suction filter and accumlator

    Copeland 3ABA series

    404A gas(assume no other, assume pure charge)

    Condition found:

    Suction line solid ice(up to 1.5'" thick) at evap-anywhere line exposed and at condensor. Where insulation stopped at condensor everything from the suction filter to the compressor service valve was solid heavy ice.

    Box temps over 0

    Unit in school so had the option to shut off unit and allow a thaw.

    Went back and pulled insulation scraps from evap output, NO txv bulb???

    Pulled side cover and "someone" had put the bulb on the mainifold. Now this manifold is made where the vertical pipe enters the horiz line like a Tee.
    The bulb was actually mounted behind the vertical pipe in the stub.!!
    Maybe 1/2 " of the bulb ever saw actual freon flow.

    Needless to say I moved the bulb out on the line at 4 o'clock, insulated it, and then reinsulated or repaired the entire suction line using 7/8x 3/4 wall.

    Figured all OK, started unit, pulled down fairly quick to 36 deg, was at end of day went home.

    This morning went back, box at 4, figured I needed to adjust thermostat, did and left. Went back tonight, 4 deg.,comp running good ice buildup on lines.

    Here are measured specs with box at 4 deg, outside air 88 deg, unit running.

    Suction 27psi
    Head 265 psi

    evap 29psi at 5 deg

    discharge line temp 132 deg
    liquid line at drier 97 deg

    comp RLA 10.0 measured 7.2

    Coils 95% clean.

    No ice build up on evap anywhere.

    Distribution lines all "frosted" the same

    compressor runs quiet, no pounding-knocking

    clear sight glass, no flashing or bubbles

    headmaster shows no sign of bleeding thru(although haven't ruled it out)

    unit will defrost with no errors, fan delay etc OK.

    Both cond and evap fans appear to be correct rpm's


    I think I listed everything .

    I won't put my ideas on the table yet.
    School starts in 2 weeks so I got to figure this thing out.

    Thanks for any help

    Andy

  2. #2
    Join Date
    Sep 2007
    Location
    NH
    Posts
    1,424
    Post Likes
    Temps right for your suction pressure.. What is the SH at the txv....

    That 5* you listed is the box temp when you took suction pressure and not the suction line temp right?

  3. #3
    Join Date
    Sep 2007
    Location
    NH
    Posts
    1,424
    Post Likes
    Wouldn't be a bad idea to pump it down or close the suction valve and see if the valves are good.

  4. #4
    Join Date
    Jul 2010
    Location
    Fishersville Va
    Posts
    31
    Post Likes
    Thread Starter
    measured psi at evap was 29

    5 deg temp was suction line 10" away from pressure port on the vertical.

    Used my new Fluke clamp probe on a reliable meter.

    I don't think there was insulation etc under clamp

    There was a bit of up/down on meter 3,4,5, all showed up.

    Pt chart in van( too tired to go get it) but this morning figured a 5 deg SH

    Did check for pressure rise when forced the thermostat, held 10psi with very slow increase.

    Andy

  5. #5
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    27# is too high for a freezer box on 404a.



  6. #6
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is offline Membership Chair/ARP Committee / Professional Member*
    Join Date
    Sep 2002
    Location
    I try to stay as far away from myself as I can.
    Posts
    37,825
    Post Likes

    I'd close the suction service valve first

    Attach a suction gauge and front-seat the suction service valve. If the suction pressure isn't 15" in a few seconds - the compressor valves are defective.

    Welded hermetic? Or iron-body hermetic?

    PHM
    --------




    Quote Originally Posted by MwTechInc View Post
    Hello

    First post , tho I read as a guest.

    Like to run this problem past other techs, I must be missing something.

    New customer, about 6 mths, no work on this unit till last week

    Walk-in freezer 10x10 system approx 6 years old

    2 fan Evap facing door

    Cond on roof, 38' run with 10' being vertical,trapped at evap.

    Cond has suction filter and accumlator

    Copeland 3ABA series

    404A gas(assume no other, assume pure charge)

    Condition found:

    Suction line solid ice(up to 1.5'" thick) at evap-anywhere line exposed and at condensor. Where insulation stopped at condensor everything from the suction filter to the compressor service valve was solid heavy ice.

    Box temps over 0

    Unit in school so had the option to shut off unit and allow a thaw.

    Went back and pulled insulation scraps from evap output, NO txv bulb???

    Pulled side cover and "someone" had put the bulb on the mainifold. Now this manifold is made where the vertical pipe enters the horiz line like a Tee.
    The bulb was actually mounted behind the vertical pipe in the stub.!!
    Maybe 1/2 " of the bulb ever saw actual freon flow.

    Needless to say I moved the bulb out on the line at 4 o'clock, insulated it, and then reinsulated or repaired the entire suction line using 7/8x 3/4 wall.

    Figured all OK, started unit, pulled down fairly quick to 36 deg, was at end of day went home.

    This morning went back, box at 4, figured I needed to adjust thermostat, did and left. Went back tonight, 4 deg.,comp running good ice buildup on lines.

    Here are measured specs with box at 4 deg, outside air 88 deg, unit running.

    Suction 27psi
    Head 265 psi

    evap 29psi at 5 deg

    discharge line temp 132 deg
    liquid line at drier 97 deg

    comp RLA 10.0 measured 7.2

    Coils 95% clean.

    No ice build up on evap anywhere.

    Distribution lines all "frosted" the same

    compressor runs quiet, no pounding-knocking

    clear sight glass, no flashing or bubbles

    headmaster shows no sign of bleeding thru(although haven't ruled it out)

    unit will defrost with no errors, fan delay etc OK.

    Both cond and evap fans appear to be correct rpm's


    I think I listed everything .

    I won't put my ideas on the table yet.
    School starts in 2 weeks so I got to figure this thing out.

    Thanks for any help

    Andy
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

  7. #7
    Join Date
    Mar 2007
    Location
    On a bull named Foo Manchu
    Posts
    18,815
    Post Likes
    Quote Originally Posted by MwTechInc View Post
    measured psi at evap was 29

    5 deg temp was suction line 10" away from pressure port on the vertical.

    Used my new Fluke clamp probe on a reliable meter.

    I don't think there was insulation etc under clamp

    There was a bit of up/down on meter 3,4,5, all showed up.

    Pt chart in van( too tired to go get it) but this morning figured a 5 deg SH

    Did check for pressure rise when forced the thermostat, held 10psi with very slow increase.

    Andy
    http://www.fridgetech.com/calculators/

    I get twice that SH with those #'s

    Was there any product in the freezer.
    “If You Can Dodge A Wrench You Can Dodge A Ball”

  8. #8
    Join Date
    Jul 2010
    Location
    Fishersville Va
    Posts
    31
    Post Likes
    Thread Starter
    Compressor is semi hermetic 3ABA-031E-TAC-222

    No product in freezer

    I may have messed up this morning doing the super heat, was in a rush.
    May have picked up the wrong number on the old chart.

    I'll go down tomorrow,check the valves, do another "superheat pressure/ temp" check to verify I've got good numbers.

    Andy
    Last edited by MwTechInc; 07-28-2010 at 11:55 PM.

  9. #9
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is offline Membership Chair/ARP Committee / Professional Member*
    Join Date
    Sep 2002
    Location
    I try to stay as far away from myself as I can.
    Posts
    37,825
    Post Likes

    pump that puppy down tomorrow -

    Start the compressor.

    Suction gauge hose on the suction service valve's access port.

    Front seat the suction service valve.

    Suction pressure should immediately head south to 15" of vacuum or more.

    If not - order a valve plate and gasket set and get it on there.

    Or - that's what I would do. <g>

    PHM
    --------



    Quote Originally Posted by MwTechInc View Post
    Compressor is semi hermetic 3ABA-031E-TAC-222

    No product in freezer

    I may have messed up this morning doing the super heat, was in a rush.
    May have picked up the wrong number on the old chart.

    I'll go down tomorrow,check the valves, do another "superheat pressure/ temp" check to verify I've got good numbers.

    Andy
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

  10. #10
    Join Date
    Dec 2006
    Location
    Litchfield,Il
    Posts
    565
    Post Likes
    I'm with stonewall. I like to run R-22 a little colder than other equipment due to the oil problems, but there is no logical reason that R-404 couldn't be used at a 2-3 degree superheat just as R-22 is. quote by jpsmith.
    --
    Jp...you were right . when i got the box temp down past 10*f my super heat settled to 2-3 deg f at the evap and 24*f at the compressor . I did achieve -10* f in the box and then set my t-stat at -5*f . MwTech...I still had ice build up at the compressor so your ok there.
    If your not getting the results you desire then change. People change from either desperation or inspiration.

  11. #11
    Join Date
    Jul 2010
    Location
    Fishersville Va
    Posts
    31
    Post Likes
    Thread Starter

    Good news today

    Ok......

    Did a pump down..............after about 30 sec the ol compressor finally pulled down to about 2"

    So needless to say a kit will be here tomorrow.

    I guess a pump down just never clicked in my brain as the gauge dropped quick when the solenoid closed.

    But in the back of my mind it seemed like the thing just couldn't pump any more

    So......we will install kit, run box, do another SH check and see what happens.

    Thanks for the help guys.

    Will update .

    Andy

  12. #12
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is offline Membership Chair/ARP Committee / Professional Member*
    Join Date
    Sep 2002
    Location
    I try to stay as far away from myself as I can.
    Posts
    37,825
    Post Likes

    sharpen your gasket scraper

    Try to scrap away from the cylinders but when you are done scraping - just bump the contactor in and all the little bits will fly out of there. Look away while you are doing this. <g>

    PHM
    --------







    Quote Originally Posted by MwTechInc View Post
    Ok......

    Did a pump down..............after about 30 sec the ol compressor finally pulled down to about 2"

    So needless to say a kit will be here tomorrow.

    I guess a pump down just never clicked in my brain as the gauge dropped quick when the solenoid closed.

    But in the back of my mind it seemed like the thing just couldn't pump any more

    So......we will install kit, run box, do another SH check and see what happens.

    Thanks for the help guys.

    Will update .

    Andy
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

  13. #13
    Join Date
    Jul 2010
    Location
    Fishersville Va
    Posts
    31
    Post Likes
    Thread Starter
    Been many years since I put a valve kit on.
    Are the torque specs included?

  14. #14
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by MwTechInc View Post
    Been many years since I put a valve kit on.
    Are the torque specs included?
    Yes, they are normally included.

    Copeland specs theirs in Inch/pounds.

    If I remember correctly, spec for a 3D compressor is 525 in/lb or 43 ft/lb



  15. #15
    Join Date
    Jul 2010
    Location
    Fishersville Va
    Posts
    31
    Post Likes
    Thread Starter

    I like neg numbers

    Installed valve kit and fired her back up.

    Sounded different, picked up discharge temp to 148.

    Down to the box for a SH check(after running a while)

    SH was 12 so a little adjusting went on and the results are:

    SH 5 , box at -2


    Will follow up next time I'm at the school to do fine tuning if necessary.

    Thanks for the help

    Andy

  16. #16
    Join Date
    Sep 2005
    Location
    florida
    Posts
    5,520
    Post Likes
    Glad to hear that the valve plate kit worked.
    I love the smell of phosgene first thing in the morning:

    To apply for professional membership click here


    Educational forums are open.

    If you would like to submit a link or an article or other related info to the EF. click here

  17. #17
    Join Date
    Jul 2010
    Location
    Fishersville Va
    Posts
    31
    Post Likes
    Thread Starter

    Fine tuning system

    Checked in on the freezer yesterday and found the box at -4 with the compressor cycling.

    I lkie things to be right on so let me pose a question.

    Still have ice formation at the condensor, now just includes the suction filter and 60 % of the accumlator.

    No ice on output of accumlator, vibration dampner or compressor.

    So things are better, however 5 miles away I just replaced the same HP Copeland on a freezer, corrected a lot of problems(other companies) and it runs perfect at 0/-2 with no ice on suction.

    Something is just not quite right.

    Now it's down to me and this system. It's only one mile from the shop so I can mess with it a lot.

    The school will be stocking the unit this week, will do a SH and check once full.

    All for now

  18. #18
    Join Date
    Feb 2008
    Location
    California
    Posts
    2,091
    Post Likes
    You will still be able to maintain box temperature with high compressor superheat...its just that compressor will thank you if you run it with a little ice to keep it cool.

    and of course it makes for a more efficient system IE: cooler vapor is more dense than warmer vapor...so your compressor would actually be doing more work per stoke.

    look at the picture in my profile...that is one happy pump.

  19. #19
    Join Date
    Oct 2008
    Location
    New Jersey
    Posts
    1,015
    Post Likes
    im kinda new to the real refrigeration part of the trade, but bein in ac my brain tells me that icing at the inlet of the compressor is bad.............im guessing that with refer its ok.......
    I dont install leaks, i just fix em

    Sig line removed by Admin*

    Lets see if this gets removed..............

  20. #20
    Join Date
    Feb 2008
    Location
    California
    Posts
    2,091
    Post Likes
    that is because most compressor manufactures recommend no less than 20* compressor superheat. Now in A/C world...you do not really run below a 35* SST, so Ice back to the compressor would mean flooding. But in Refer world..we deal with much lower SST's such as -25,-20,-15,-10...while running such low SST's and trying to maintain that minimum 20* compressor superheat, it becomes obvious why we would expect to see ice back to a compressor. I will go out on a limb and say that if you are running a -25SST and do not have ice on the compressor...you have a problem.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •