    19XRV bearing ispection.

    Have a 2004 19XRV 680 ton with 14K hours on it, never really surged much, and oil samples have been looking good. OEM rep wants to talk about a bearing inspection, but I really feel it's too early to throw that kind of money at it.
    We're gonna talk anyway next week, so I was wondering what every one else thinks about it. I haven't been to any tear down schooling on this machine. Personally, I think it could go a while yet.

    Thanks to all.
    God Bless our Veterans

    God Bless the USA

  2. #2
    Join Date
    Mar 2010
    Location
    Morgan Hill Ca.
    Posts
    1,380
    Post Likes
    My personal feelings on it are.....If there is nothing pointing you to check the bearing wear, why check for bearing wear?

    Seriously, I would rather see the money spent on a vibration analysis and maintenance....

    Good oil samples, good oil pressure, no obvious system issues...


    LET HER BUCK!

    GT Jets
    If a day goes by and you have learned nothing, I hope you got a lot of sleep.

  3. #3
    Join Date
    Nov 2008
    Posts
    367
    Post Likes
    Some of those machines have roller brgs. in the high speed.

    You would need vibration trending to check.

  4. #4
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    8,215
    Post Likes
    The Tin level in the oil samples should tell you when its time to inspect.

  5. #5
    Join Date
    Nov 2008
    Posts
    367
    Post Likes
    Quote Originally Posted by pecmsg View Post
    The Tin level in the oil samples should tell you when its time to inspect.
    I would say that depends on what high speed you have in the machine.

  6. #6
    Join Date
    May 2001
    Location
    Western Wa
    Posts
    2,025
    Post Likes
    This one is the standard bearings and Kingsbury thrust
    God Bless our Veterans

    God Bless the USA

  7. #7
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    11,469
    Post Likes
    I have a 19XR at work with over 28k on the clock. Oil was changed last year after the oil pump faltered. This year's oil report came back good. Other two machines ~25k and also had good reports. Nobody's talking about a teardown for any of these machines in the near future.
    Building Physics Rule #1: Hot flows to cold.


    Building Physics Rule #2:
    Higher air pressure moves toward lower air pressure


    Building Physics Rule #3:
    Higher moisture concentration moves toward lower moisture concentration.

  8. #8
    Join Date
    Sep 2007
    Location
    Somewhere in the world.
    Posts
    1,661
    Post Likes
    Check page 74 they talk about recommendations for bearings.
    Attached Files Attached Files
    A mind is like a parachute. It doesn't work if it is not open.

    The best part of going to work is coming back home at the end of the day.

    Hard work spotlights the character of people: some turn up their sleeves, some turn up their noses, and some don't turn up at all.

  9. #9
    Join Date
    May 2001
    Location
    Western Wa
    Posts
    2,025
    Post Likes
    Tin is creeping up and was at 9PPM the last test almost a year ago, so it's time, I think, if not this winter, the next. Aluminum, iron, moisture, and acid number were real good. Depends on what management can spend on it and when. Carrier's upper limit on tin is 15PPM.
    God Bless our Veterans

    God Bless the USA

  10. #10
    Join Date
    Sep 2007
    Location
    Somewhere in the world.
    Posts
    1,661
    Post Likes
    Hopefully they won't wait to long best of luck.
    A mind is like a parachute. It doesn't work if it is not open.

    The best part of going to work is coming back home at the end of the day.

    Hard work spotlights the character of people: some turn up their sleeves, some turn up their noses, and some don't turn up at all.

  11. #11
    Join Date
    Mar 2009
    Posts
    3
    Post Likes
    Problem 19XR unit with alarm 206 or Benshaw panel alarm #73.
    After alarm 206 (Starter Fault) , reset alarm and start again than chiller run only 30-40 sec and cut off again with same alarm 206.
    But if we shutdown the unit for 12 hours and tommorrow we start will normal for 7-8 hours and alarm 206 comes out again.
    Please advise us for this matter.

  12. #12
    Join Date
    Mar 2009
    Posts
    3
    Post Likes

    19XR unit with alarm 206

    Problem 19XR unit with alarm 206 or Benshaw panel alarm #73.
    After alarm 206 (Starter Fault) , reset alarm and start again than chiller run only 30-40 sec and cut off again with same alarm 206.
    But if we shutdown the unit for 12 hours and tommorrow we start will normal for 7-8 hours and alarm 206 comes out again.
    Please advise us for this matter.

  13. #13
    Join Date
    May 2001
    Location
    Western Wa
    Posts
    2,025
    Post Likes
    Trying to get funding for a high speed inspection.

    If that doesn't work out, the plan would be to change oil and then closely monitor.
    Had a vibration analysis, and there is some indication of vibration, but not threatening, according to my OEM brain trust.
    God Bless our Veterans

    God Bless the USA