    High Suction Press.

    Im sure this is supposed to go in the pro forum but I dont have quite enough post yet. Hopefully after this thread I will be able to apply.

    Im working on a Goodman Packaged roof top. I think I know the problem but would like to hear some input from some of you guys.

    Return temp 80
    Supply temp 70
    Suction Press 92
    Discharge Press 260
    Superheat 22
    Subcool 6

    The unit has two systems. Each one 5 tons. Each one running the same readings (with in +/- 2 degrees on superheat and sub) I adjusted txv to bringdown superheat but as I did that the suction press went up and the delta across the coil dropped (got down to about 4 degrees delta with a superheat of 10)

    Anythoughts are greatlly appreciated!

  2. #2
    Join Date
    Jul 2010
    Location
    Andalucia
    Posts
    3,210
    Amp draw?, OAT? Cond. coil clean? Pressures on both circuits?Wetbulb? Filters clean? Can't have too much info.Always a good habit to have too much info when you need help.
    "War is cruelty,and you cannot refine it." Sherman to the leadership of Atlanta prior to burning the city.

    "Common sense is the collection of prejudices acquired by age eighteen."
    Albert Einstein

    Romney campaign: "We're not going to let our campaign be ruled by fact-checkers,"

    Lindsey Graham: “We’re not generating enough angry white guys to stay in business for the long term.”

  3. #3
    Join Date
    Apr 2010
    Posts
    27
    Quote Originally Posted by pageyjim View Post
    Amp draw?, OAT? Cond. coil clean? Pressures on both circuits?Wetbulb? Filters clean? Can't have too much info.Always a good habit to have too much info when you need help.
    Amp draw comp1 L1=17 L2=16.5 L3=16
    comp2 L1=19 L2=17 L3=17

    OAT DB=95
    WB=80

    Cond coil clean? yes
    Press on both circuits
    Suction1=92 discharge1=260
    Suction2=93 discharge2=270

    Wet Bulb Return=68
    Supply=64

    Filters Clean? yes
    Can't have too much info. SORRY!
    Always a good habit to have too much info when you need help. Thanks for the advice!

  4. #4
    Join Date
    Jun 2006
    Location
    New Jersey
    Posts
    4,126
    Quote Originally Posted by vernilla View Post
    Im sure this is supposed to go in the pro forum but I dont have quite enough post yet. Hopefully after this thread I will be able to apply.

    Im working on a Goodman Packaged roof top. I think I know the problem but would like to hear some input from some of you guys.

    Return temp 80
    Supply temp 70
    Suction Press 92
    Discharge Press 260
    Superheat 22
    Subcool 6

    The unit has two systems. Each one 5 tons. Each one running the same readings (with in +/- 2 degrees on superheat and sub) I adjusted txv to bringdown superheat but as I did that the suction press went up and the delta across the coil dropped (got down to about 4 degrees delta with a superheat of 10)

    Anythoughts are greatlly appreciated!
    So you have 22 degrees SH on a 92psi suction line. So you line temp is about 85 degrees. So your suction line is hotter than your return air? Is this a HP? You have HGP?

  5. #5
    Join Date
    Jul 2010
    Location
    Andalucia
    Posts
    3,210
    Quote Originally Posted by vernilla View Post
    Amp draw comp1 L1=17 L2=16.5 L3=16
    comp2 L1=19 L2=17 L3=17

    OAT DB=95
    WB=80

    Cond coil clean? yes
    Press on both circuits
    Suction1=92 discharge1=260
    Suction2=93 discharge2=270

    Wet Bulb Return=68
    Supply=64

    Filters Clean? yes
    Can't have too much info. SORRY!
    Always a good habit to have too much info when you need help. Thanks for the advice!
    No need to be sorry but always good advice esp. if its your boss or tech support.
    Amp draw is given but you didn't show RLA which is on nomenclenture plate. But that is probably not the problem since both are close.
    Are you drawing in an excess of outdoor air? Economizers stuck open? You may think the condenser coil is clean but it mat not be.
    Check TXV feeler bulb is insulated and mounted right.
    When you take your measurements are you opening a panel that effects the airflow over the condenser?
    "War is cruelty,and you cannot refine it." Sherman to the leadership of Atlanta prior to burning the city.

    "Common sense is the collection of prejudices acquired by age eighteen."
    Albert Einstein

    Romney campaign: "We're not going to let our campaign be ruled by fact-checkers,"

    Lindsey Graham: “We’re not generating enough angry white guys to stay in business for the long term.”

  6. #6
    Join Date
    Sep 2008
    Location
    Delaware
    Posts
    243
    I'm in Delaware and know what kind of weather we are having here and probably there! We are at or above design conditions a lot this year. Whats chances that you have more load than you have machine? Do things fall into line after cooling down at night ? You have two circuits exibiting the same problems. Look for the common denominator (ambient maybe)? Water on condensers?

  7. #7
    Join Date
    Jun 2010
    Location
    U.A. (upper Alabama)
    Posts
    734
    Sounds to me also, that you have too much load on your evap. Prob why subcooling is low, because your TEV is wide open trying to get superheat down. I know this sounds crazy, but I would try to add some gas and get subcooling right, then superheat might drop and in turn TEV is going to pinch off to lower suction press. and saturation temp.

  8. #8
    Join Date
    Apr 2010
    Posts
    27
    Quote Originally Posted by pageyjim View Post
    No need to be sorry but always good advice esp. if its your boss or tech support.
    Amp draw is given but you didn't show RLA which is on nomenclenture plate. But that is probably not the problem since both are close.
    Are you drawing in an excess of outdoor air? Economizers stuck open? You may think the condenser coil is clean but it mat not be.
    Check TXV feeler bulb is insulated and mounted right.
    When you take your measurements are you opening a panel that effects the airflow over the condenser?
    No economizer on this unit.

    Txv bulb is insulated but not to my standards. It is foam taped but could be effected by the air stream. I dont think it would be the cause of the problem being that it ran that way in the past.

    The panel that is removed for readings doesnt effect the condenser flow.

  9. #9
    Join Date
    Apr 2010
    Posts
    27
    Quote Originally Posted by Chiller Guy View Post
    I'm in Delaware and know what kind of weather we are having here and probably there! We are at or above design conditions a lot this year. Whats chances that you have more load than you have machine? Do things fall into line after cooling down at night ? You have two circuits exibiting the same problems. Look for the common denominator (ambient maybe)? Water on condensers?
    Thought about that but I think it should still have more than a 10 degree delta?

  10. #10
    Join Date
    Apr 2010
    Posts
    27
    Quote Originally Posted by cperk View Post
    Sounds to me also, that you have too much load on your evap. Prob why subcooling is low, because your TEV is wide open trying to get superheat down. I know this sounds crazy, but I would try to add some gas and get subcooling right, then superheat might drop and in turn TEV is going to pinch off to lower suction press. and saturation temp.
    I think that is my next move. Just kinda has me confused with the high suction. That goes againt everything that I've been taught.

    Low suction=low charge and visa versa??

  11. #11
    Join Date
    Jul 2004
    Location
    Maryland
    Posts
    333
    Quote Originally Posted by ascj View Post
    So you have 22 degrees SH on a 92psi suction line. So you line temp is about 85 degrees. So your suction line is hotter than your return air? Is this a HP? You have HGP?

    I would be tempted to pull enough refrigerant out to cause your liquid line to be at saturation then i would take a liquid line temp to compare it to your saturation temp. If there not close recover refrig and start over with virgin refrig.
    As stated something doesnt sound right with your suction pressure and suction SH. SH is about spot on copeland would like A Min of 20 at the compressor. If you are taking this at the comp that shows your TXV is doing its job, and you have adequate sub cooling maybe not design.
    As stated I would be looking hard for a hot gas bypass

  12. #12
    Join Date
    Jun 2010
    Location
    U.A. (upper Alabama)
    Posts
    734
    Quote Originally Posted by cperk View Post
    Sounds to me also, that you have too much load on your evap. Prob why subcooling is low, because your TEV is wide open trying to get superheat down. I know this sounds crazy, but I would try to add some gas and get subcooling right, then superheat might drop and in turn TEV is going to pinch off to lower suction press. and saturation temp.
    Are the comps. on totally diff. circuits? Or are the comps.on same circuit?

  13. #13
    Join Date
    Apr 2010
    Posts
    27
    Quote Originally Posted by cperk View Post
    Are the comps. on totally diff. circuits? Or are the comps.on same circuit?
    Different circuits.