    Jul 2010
    Chicago Suburbs, IL
    Calculating Cooling Capacity of AC Units
    This company im working for hasn't done an audit of their HVAC system in 20+ years. They have a bunch of Modine CSC-1515 units in their warehouse that were manufactured in the mid 60's.
    I have little experience in the HVAC field, and few resources at my disposal (Manual N for Load Calcs). I have the Design Specs of the units from a previous audit, but would like to calculate the Cooling Capacity of each unit and am having difficulty calculating the BTUH / Tons refrigeration output.
    Any help with equations or references to such is appreciated.
    Thanks.
    Apr 2006
    s.c.
    CFM X Delta HT X 4.5 = total cooling btu
    Return WB of 61.7= 27.62 btu's per lb of dry air (plotted on pycrometric chart)
    Supply WB of 54.2= 22.74 btu's per lb of dry air (plotted on pycrometric chart)
    Subtact the two and you get 4.88 that is you Delta HT
    So lets say 1000 cfm X 4.88 X 4.5= 21,960 BTU
    1000CFM X 4.88 = 4880 X 4.5 = 21,960 Total BTUs removed.
    1000CFM X (16°Delta X 1.08) = 17,280 Sensible BTUs removed.
    21,960 - 17280 = 4,680 BTUs Latent removed.
    measuring indoor cfm for gas-oil heat
    cfm= btuh output divided ( 1.08 x delta temp. )
    measuring indoor cfm for electric heat
    cfm= volts x amps x 3.414 divided ( 1.08 x delta temp. )
    Apr 2006
    s.c.
    best cfm measurement is a tesp measurement and match it to the blower performance chart