    I installed a new 5 ton condenser unit at a daycare center. Pressure test fine, vaccume held 24hrs. Opened king valves then started the unit. Compressor sounds like a jack hammer and my guages do not show a change in pressure. Any help? This is a 3 phase unit and the compressor was pulling 11 amps when i pulled the power.

  2. #2
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    34,057
    scroll running backwards. reverse 2 leads of the incoming power.

  3. #3
    Join Date
    Mar 2003
    Location
    Washington,NJ
    Posts
    504
    Sounds like you need to change the electrical input phasing to the unit.

  4. #4
    Join Date
    Sep 2001
    Location
    East Stroudsburg, PA
    Posts
    13,215
    Originally posted by BaldLoonie
    scroll running backwards. reverse 2 leads of the incoming power.
    Yeah. This is true.

    It's in the I&O manual, kid.

  5. #5
    Join Date
    Oct 2001
    Posts
    6,956
    next time bump the condenser fan if 3 phase for top discharge of the air,or push the compressor contactor in next time for 10 seconds and grab the suction if you feel the slightest heat reverse the 2 leads.