07-03-2010, 12:59 PM #1
PCV-3J-C1-D2
Anyone have a manual they could share?
-
07-03-2010, 03:06 PM #2
Professional Member t-bad email address
- Join Date
- Sep 2005
- Location
- chiller plant
- Posts
- 49
you got mail , pcv m-1 manual
-
07-03-2010, 05:07 PM #3
You made my week ,thank you so much!
-
07-03-2010, 06:02 PM #4
Professional Member
- Join Date
- Sep 2008
- Location
- Delaware
- Posts
- 243
My God man that thing is older than dirt. What is the serial #. They are (were) good, solid machines. Any particular problem or just need maint info?
-
07-03-2010, 06:30 PM #5
serial number is LSF19764. I think previous contractor over charged it , I can see refrigerant carry over in the second stage sight glass sounds like liquid hitting the impeller. Shut the machine down and checked shut down level. Refrigerant was above the sight glass on the evap. Pulled out 250 lbs, to about 2/3rd of sight glass. Unable to load it up to check approach at design capacity Due to low side surge.
I have a very high approach at partial load. So I think i am going to drop the evap head inspect and brush the tubes I think i
Anyone know design pressure drop on evap and condenser?
Is it possible to have liquid refrigerant overflowing the economizer into the second stage, that line was very cold as well as the second stage at the sight glass? Since removing refrigerant seems to have taken care of the carry over liquid for the economizer. Any thoughts are welcome as i am very unfamiliar with these tranes.
The manual is a big help i can see i didnt do the shut down level check correctly. If anything i may still be slightly overcharged, after cleaning the evap tubes i will get a better approach reading
I have no idea how i get the icon of the fellow eating popcorn lol
-
07-03-2010, 07:16 PM #6
good question
i would assume that under low load conditions liquid could carry over from the top of the economizer into the second stage igv????????
but i would think at that point there would be liquid carry over at the first stage also??????????
i would like to know how that goes!
FrankI WILL SELL WORK,GENERATE BUSINESS, GO GET NEW CUSTOMERS!
YOU SHUT THE HELL UP AND QUIT RUNNING YOUR MOUTH!
-
07-03-2010, 07:18 PM #7
if you have a high approach at low load you will have a very high approach at high load!!!!!!!!!!!!!!!!
I WILL SELL WORK,GENERATE BUSINESS, GO GET NEW CUSTOMERS!
YOU SHUT THE HELL UP AND QUIT RUNNING YOUR MOUTH!
-
07-04-2010, 01:54 AM #8
your s/n is probably a 'L5' or 'L6' instead of an 'LS'
if it is a 2 pass evaporator and a 2 pass condensor, then at 95F condensor leaving and 44F evaporator leaving, you are looking at approximately 385 tons @ 318 kW (with water). 780# R11 charge, 7 gallons of oil. if you have an 'RPS' motor (listed on the motor nameplate) then your charge would be 820# R11.
evaporator, WATER: minimum flow: 292 gpm @ 2.85 feet, maximum: 1,070 gpm @ 27.50 feet
condensor, WATER: minimum flow: 364 gpm @ 2.00 feet, maximum: 1,337 gpm @ 21.00 feetThe weak aren't destroyed by the strong.
The weak are destroyed by the under-estimated.
I know a famous song that ends in 'my nose'. The artist is dead. Know who?
-
07-04-2010, 02:13 AM #9
I am impressed, thank you sir
-
07-04-2010, 08:04 AM #10
Professional Member
- Join Date
- Sep 2008
- Location
- Delaware
- Posts
- 243
Jayguy beat me with the numbers for the unit but I agree. I think it is a 75 or 76 vintage unit. I beleive C1 -D2 indicates the flow arrangement for the tube bundles. Do you have a single pass evap? Carryover sounds like BB's hitting the wheel and the volute will be cold in the area down under the purge and above the oil sump (practice the laying on of hands).You may have an oil fouled evap causing the carryover. Pulling/distilling and weighing in the charge may be a good starting point IF time allows. Of course fouled tubes are always an issue but usually evap tubes do not get fouled on the water side as its a closed system (hopefully).
Any history on the unit yet? Still running R-11? What changes (if any) have been made? Rebuilds? Last time seals were looked at? and on, and on, etc.
Remember K-I-S-S. Check all the easy things first
-
07-04-2010, 09:14 AM #11
The machine was rebuild in the early 90s and then again it may have been rebuild a few years ago last part i havent confirmed.
Definitely sounds like liquid hitting IGV or impeller. I notice the sound together with a surge. liquid splashing up on the 2nd stage sight glass, economizer line to second stage very cold . Discharge off the second stage into the condenser radically drops in temperature. Has anyone measured discharge superheat on these machines at design conditions?
Just curious A oil saturated evap, will have a high approach but a low discharge superheat? Time is an issue but i really want to get this chiller right . So i will probably pull the evap heads and refrigerant charge and attempt to distill. Thank you for your help guys, I am having a blast around this old machine. Playtime will be over if i dont get it right lol
-
07-04-2010, 10:51 AM #12
-
07-04-2010, 11:19 AM #13
Professional Member
- Join Date
- Sep 2008
- Location
- Delaware
- Posts
- 243
Stickerhead.
I converted one of those 1958 models to R-123 for Du Pont. We tore everything off but the shells and bundles and installed a "Tri-Star " conversion. They were built like tanks and weighed about the same.
That was 15-20yrs ago +/- and as far as I know its still running.