    Confused trouble with split system. low suction.

    Got a trane split system that's about 10 years old that I was sent to change the compressor on just because the town maint. Guy wanted to. Changed it then charged system and problems popped up. First of all the condenser is oversized. 5 ton and ahu is 3.5 ton. Wtf. Suction pressure is low 43 psig.70 ambient temp. 200 psig liquid press. Have 22 superheat at evap and 19 subcooling.28 delta tee across evap. Kindahigh airflow. What will happen with an oversized condenser ? Please help. Txv system

  2. #2
    Join Date
    Mar 2005
    Posts
    13,077
    Post Likes

  3. #3
    Join Date
    May 2000
    Location
    Colorado flatland native
    Posts
    15,068
    Post Likes
    you contractor kemosabe?
    My doctor gave me six months to live, but when I couldn't pay the bill he gave me six months more.
    Walter Matthau

  4. #4
    Join Date
    Feb 2006
    Location
    Tn.
    Posts
    1,346
    Post Likes
    I dont know

  5. #5
    Join Date
    Feb 2006
    Location
    Tn.
    Posts
    1,346
    Post Likes
    Quote Originally Posted by m-cooling View Post
    I dont know
    But I would guess you have voided any warranty you had

  6. #6
    Join Date
    Jul 2010
    Location
    connecticut
    Posts
    9
    Post Likes
    Thread Starter
    Yes I'm a contractor. Warranty is out the window. Just curious of symptoms associated with this.

  7. #7
    Join Date
    Jul 2010
    Location
    connecticut
    Posts
    9
    Post Likes
    Thread Starter

    Thumbs up

    Quote Originally Posted by the dangling wrangler View Post
    U should be the last person to talk. I can also think your a 15 years old by your posts. No.... you must be 15.

  8. #8
    Join Date
    Mar 2005
    Posts
    13,077
    Post Likes
    Quote Originally Posted by bora 18t View Post
    U should be the last person to talk. I can also think your a 15 years old by your posts. No.... you must be 15.
    I guess you told me.
    Last edited by beenthere; 07-03-2010 at 02:36 PM. Reason: Inappropriate comment in image

  9. #9
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    I like these humorous threads.

    How would a home owner know what delta T is? Many by reading on this forum.
    Same as for SH, SC, Approach, CTOA, DB, WD, DP, ESP, TESP, Th, and a several other abreviations.

  10. #10
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Bora.

    It helps if you fill out your profile.

    Get your post count up to 15 and apply for pro membership. Once accepted, you'll have access to the pro forums. Where we sometimes talk at great lengths about these types of things. And sometimes, we even talk about technical things in the technical forum.

  11. #11
    Join Date
    Aug 2007
    Location
    Winter Haven, FL
    Posts
    4,380
    Post Likes
    Everyone knows that all you need to do is adjust the subheat reading to make it work.

  12. #12
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    While some of the Pro members have answered in a less then complimenting manor. Which can be taken wrong by many.

    They do know what they are talking about. And are well respected.

    Please don't change their names to insults.

    I have edited some post.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •