    Confused trouble with split system. low suction.

    Got a trane split system that's about 10 years old that I was sent to change the compressor on just because the town maint. Guy wanted to. Changed it then charged system and problems popped up. First of all the condenser is oversized. 5 ton and ahu is 3.5 ton. Wtf. Suction pressure is low 43 psig.70 ambient temp. 200 psig liquid press. Have 22 superheat at evap and 19 subcooling.28 delta tee across evap. Kindahigh airflow. What will happen with an oversized condenser ? Please help. Txv system

  2. #2
    Join Date
    Mar 2005
    Location
    Houston, Texas
    Posts
    11,873

  3. #3
    Join Date
    May 2000
    Location
    Colorado flatland native
    Posts
    15,067
    you contractor kemosabe?
    My doctor gave me six months to live, but when I couldn't pay the bill he gave me six months more.
    Walter Matthau

  4. #4
    Join Date
    Feb 2006
    Location
    Tn.
    Posts
    1,344
    I dont know

  5. #5
    Join Date
    Feb 2006
    Location
    Tn.
    Posts
    1,344
    Quote Originally Posted by m-cooling View Post
    I dont know
    But I would guess you have voided any warranty you had

  6. #6
    Join Date
    Jul 2010
    Location
    connecticut
    Posts
    9
    Yes I'm a contractor. Warranty is out the window. Just curious of symptoms associated with this.

  7. #7
    Join Date
    Mar 2005
    Location
    Houston, Texas
    Posts
    11,873
    If you're a contractor, why knowingly do something that's wrong?
    A job like this, you should have walked away from. Or, made them do it right.
    Hope you got paid in advance.

  8. #8
    Join Date
    Jul 2010
    Location
    connecticut
    Posts
    9

    Frown

    Quote Originally Posted by the dangling wrangler View Post
    If you're a contractor, why knowingly do something that's wrong?
    A job like this, you should have walked away from. Or, made them do it right.
    Hope you got paid in advance.
    Why r u jumping on me if u don't know the story. All I want is answer to question.not u questioning the job. If u need to know I was sent to the job to replace the compressor somebody else shot down a year ago. I replaced it like I was told then while running it I found problem.

  9. #9
    Join Date
    Mar 2005
    Location
    Houston, Texas
    Posts
    11,873
    Quote Originally Posted by bora 18t View Post
    Why r u jumping on me if u don't know the story. All I want is answer to question.not u questioning the job. If u need to know I was sent to the job to replace the compressor somebody else shot down a year ago. I replaced it like I was told then while running it I found problem.
    Fair enough. I'll answer your question.
    Your never gonna make this frankenunit work.
    Good Luck to ya though.

  10. #10
    Join Date
    Jul 2006
    Location
    Anytown USA
    Posts
    2,060
    Heres your answer.


    5 ton condenser + 3.5 ton coil and Air handler= not enough airflow.

  11. #11
    Join Date
    Jul 2010
    Location
    connecticut
    Posts
    9

    Thumbs up

    Which would b low suction, high delta t across evap, low head, high superheat. Nice. Now they have to replace everything. Wow.

  12. #12
    Join Date
    May 2000
    Location
    Colorado flatland native
    Posts
    15,067
    Quote Originally Posted by bora 18t View Post
    Why r u jumping on me if u don't know the story. All I want is answer to question.not u questioning the job.

    You should already know the answer to this bub. There are no right answers without complete information. See what happened to you?"

    If u need to know I was sent to the job to replace the compressor somebody else shot down a year ago. I replaced it like I was told then while running it I found problem.
    You have the ol "did the job before I looked at the system" alligator bite you on the ass enough times, you will learn the value of complete info every time.
    My doctor gave me six months to live, but when I couldn't pay the bill he gave me six months more.
    Walter Matthau

  13. #13
    Join Date
    Mar 2005
    Location
    Houston, Texas
    Posts
    11,873
    Quote Originally Posted by bora 18t View Post
    Which would b low suction, high delta t across evap, low head, high superheat. Nice. Now they have to replace everything. Wow.
    Hate to be the bearer of bad news but, you sir are not an Air Conditioning contractor.

Page 1 of 3 123 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event