Thread: R-22 Walk in cooler

  1. #1
    Join Date
    Jul 2004
    Location
    Bennettsville, SC
    Posts
    248
    Post Likes
    sorry to post another walk-in cooler problem here,but hoping for some help here...
    keep in mind i mostly do residential work

    outdoor condensing unit:copeland model#F3AH-A100-CAV-001
    indoor evap. unit:BOHN model#adt070ak
    indoor txv:Sporlan KT 43 VC
    76.4 F outdoor temp
    38 F inside cooler temp
    suction pressure:49 psi head pressure:200 psi
    suction saturation temp:25 head saturation temp:100
    suction line temp:47.3 head line temp:91.4
    **unit uses a thermostat set at 36 F**
    problem is, as you can tell the superheat is way high and over a period of a week the indoor coil is frozen up solid. I've tried adjusting the txv in both directions from factory settings and the best I can achieve is 20-22 superheat. Tried to adjust it by adding and taking away freon (oh yea i forgot to mention it's a R-22 system), finaly got frustrated and recovered all freon from system and recharged until site glass just was clear and then tried to adjust the superheat yet again by the txv with the same results. Any help with this situation would be greatly appreciated. If I have left out any needed info. please let me know.

  2. #2
    Join Date
    Jan 2004
    Location
    Earth
    Posts
    4,880
    Post Likes
    You gave us the powerhead of the valve but not the size. Sounds like it may be to small, or your strainer is clogging. Is the valve body icing?
    A Diamond is just a piece of coal, that made good under pressure!

  3. #3
    Join Date
    Jul 2004
    Location
    Bennettsville, SC
    Posts
    248
    Post Likes
    Thread Starter
    srry...should have wrote it like this
    BOHN (heatcraft) model #ADT070AK

  4. #4
    Join Date
    Jul 2004
    Location
    Bennettsville, SC
    Posts
    248
    Post Likes
    Thread Starter
    no the valve body is not icing. i start seeing frost at the distributer and the first 2 loops of the evaporator.

    it doesnt seem to go any further while im there, but if i come back in a few days its frosted at least the whole coil and frozen up solid within a week

  5. #5
    Join Date
    Jan 2004
    Location
    Earth
    Posts
    4,880
    Post Likes
    That’s the coil size, what’s the valve size (Tonnage).
    A Diamond is just a piece of coal, that made good under pressure!

  6. #6
    Join Date
    Jul 2004
    Location
    Bennettsville, SC
    Posts
    248
    Post Likes
    Thread Starter
    not sure...we didnt install the unit and the #'s i gave are the only ones i could find on the valve...is there another way to tell?¿?¿

  7. #7
    Join Date
    Jan 2004
    Location
    Earth
    Posts
    4,880
    Post Likes
    If its not on the powerhead, it should be stamped on the valve body. If it's a Q body there may be a silver tag on the cap tube.
    A Diamond is just a piece of coal, that made good under pressure!

  8. #8
    Join Date
    Jul 2004
    Location
    Bennettsville, SC
    Posts
    248
    Post Likes
    Thread Starter
    the valve is in a position that is very easy to see all sides of it and there are no other visible #'s on it or around it and there is no trace of any silver tags

  9. #9
    Join Date
    Oct 2002
    Location
    Southeast Ohio
    Posts
    517
    Post Likes
    Where are you reading your suction line temperature and your pressure reading. You should have 6°to 10°superheat at the expansion valve bulb but if you are reading the suction line temp at the compressor copelands recommendation is 20° at the compressor

  10. #10
    Join Date
    Jul 2004
    Location
    Bennettsville, SC
    Posts
    248
    Post Likes
    Thread Starter
    i was told 12 degrees at the compressor by our supplier, but i suppose they may be wrong...were did you find ur info at¿

  11. #11
    Join Date
    Aug 2004
    Location
    Des Moines, IA
    Posts
    76
    Post Likes

    R-22 Walk in

    40 degree suction line temop at compressor, or max of 240 degree? within 6 inches of discharge. Hermetic or semi? 12degree superheat at txv, possibly down to 4 degree depending on line length. add for pressure drop. Sporlan and alco will be stamped with tonage. Recommend, Depending on location of stat bulb, running box too cold. Insall a stat that read evap temp,say 37 degree constant cut in with specific differincial or install a time clock to shut down system for 1 to 11/2 hour each night.

  12. #12
    Join Date
    Aug 2004
    Location
    Des Moines, IA
    Posts
    76
    Post Likes

    Hmm

    I'm new so a response would be appreciated

  13. #13
    Join Date
    Jul 2002
    Location
    hamilton ont can
    Posts
    109
    Post Likes
    take out tstat and replace with lo press control. set it at 37#to 40# cut in and about 61# cut outto start. then measure box temp to fine tune press control. be sure to set cut in high enough to defrost coil. this takes some time but it works. i have done this many times with great sucess

    good luck

  14. #14
    Join Date
    Aug 2004
    Location
    Des Moines, IA
    Posts
    76
    Post Likes
    Unless condeser is in an ambient cotrolled ambient out doors, a low preessure control will not give adequet results.

  15. #15
    Join Date
    Aug 2004
    Location
    chicago
    Posts
    123
    Post Likes
    Originally posted by psmurf
    take out tstat and replace with lo press control. set it at 37#to 40# cut in and about 61# cut outto start. then measure box temp to fine tune press control. be sure to set cut in high enough to defrost coil. this takes some time but it works. i have done this many times with great sucess

    good luck
    i asked in the topic i started about the LPC settings i have it at 32CO and 64CI, that i got from a frefrigerant table the yellow laminated card by alco controls, why did someone say to set the cutout at 5 and cut in at 25, maybe he didnt see it was R22

    but did you take the discharge line off of the txv and inspect the screen when you evacuated the system

  16. #16
    Join Date
    Aug 2004
    Location
    Des Moines, IA
    Posts
    76
    Post Likes
    Unless condeser is in an ambient cotrolled ambient out doors, a low preessure control will not give adequet results.

  17. #17
    Join Date
    Aug 2004
    Location
    Des Moines, IA
    Posts
    76
    Post Likes
    Post 9: backward but OK if condenser is indoors, otherwise, is there pump down?

  18. #18
    Join Date
    May 2004
    Posts
    14,135
    Post Likes
    prestiege

    i asked in the topic i started about the LPC settings i have it at 32CO and 64CI, that i got from a frefrigerant table the yellow laminated card by alco controls, why did someone say to set the cutout at 5 and cut in at 25, maybe he didnt see it was R22

    LPC set at 5lbs in and 25lb out is for LLV (pump down, not temp/pressure control)

    I think you were peeking at another post

    32lbs cut out w/ R-22 = 10* too low!




  19. #19
    Join Date
    Aug 2004
    Location
    Des Moines, IA
    Posts
    76
    Post Likes
    powt 14 Info comes from copeland engeneering manuals,basic refri( not trying to be ruud), Maintain minimum superhaet to maintain minimum discharge temp, to be > ? temp. Can't rem exactt #

  20. #20
    Join Date
    Jul 2004
    Location
    Bennettsville, SC
    Posts
    248
    Post Likes
    Thread Starter
    i believe i misled you when i stated i had removed the freon...what i meant is i blew it back into a recover cylinder straight from manifold until i began to see the sight glass half empty. then i began adding freon until the sight glass just was full. i do apoligise for my misleading u to what i had done...i also failed to mention that the unti also has a lpc however i did not pay attention to what they were set at(i was trying to figure out why i felt as if i could not get the superheat right) i was taking my line temp readings from 6" away from the compressor as recommended by copeland in their faq section; here is there exact quote from that page (Superheat at the compressor should be checked at the compressor only. Take the suction pressure at the service valve and convert it to saturation temperature. Compare this to the actual temperature obtained approximately six inches out on the suction line.)

    i will check the lpc settings and once again see if i can find anymore #'s on the txv, tomorrow when i return to finish
    However going by the method that copeland says for checking the superheat i still do not understand why i cant get the superheat down anymore?¿

    on another note:i found this particular and very useful site while looking for answers to my dilemma that may be helpful to everyone if you havent already seen it
    http://www.brainerdcompressor.com/tech_data.htm

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •