Thread: TXV sizing
    NJ
    Could you tell me the effects/signs of a wrongly sized expansion valve?
    Jun 2001
    San Diego, CA
    undersized: high subcool, high superheat, low deltaT on evap, localized icing of evap coil likely.
    oversized: low deltaT on evap, low superheat, compressor
    damage likely especially during low load/ high ambient
    conditions.
    NJ
    conditions.
    The only part I can`t comprehend is how can there be low superheat with low delta T on evap.By delta T do you mean air across evap.or air to refrigerant?
    South Dakota
    Undersized TEVs starve the evaporator while oversized TEVs hunt and may eventually slug the compressor.
    Earth
    A lot of spoiled product, and one P.O.ed customer.
    Jun 2001
    San Diego, CA
    altan, you're right
    but in an excessively overfed evap - flash gas isn't being
    evenly distributed across the coil. Some flashing occurs in the suction line, hence a low air split deltaT. Not always, only in extreme cases.