    I am working on a 5ton York condensing unit(TXV) head pressure is 80 psig , suction is 10 psig,the liquid line is very cold and sweating, the system is not low on R22.

    What do you think?

  2. #2
    Join Date
    Jul 2004
    Post Likes
    Sounds like a restriction, try to find the place on the liquid line where the sweating begins, that will be the likely location of the problem.

  3. #3
    Join Date
    Aug 2003
    Post Likes
    Check for a restriction at the liquid line drier. Unit may have a factory installed drier on the liquid line inside the unit.