    Carrier 38AKS028...600, 06E compressor. Trying to verify subcooling, but interior load causing compressor to unload. Compressor has two pressure activated unloaders. Any effect or does SC stay constant? Running about 7* at this time, no receiver, sight glass full. Split air handlers with dual LLS on each, only 1 circuit calling at this time on each AH. SH running 18* at compressor. I think I'm still low, but am sweating back and don't want to thin out the oil.

  2. #2
    Join Date
    May 2004
    Posts
    1,462
    Unit must be loaded to check charge.
    If all else fails....Try reading the directions!

    Tell it like it is and let the chips fall where they may.

    Any views or opinions stated here are strictly my own.


  3. #3
    cant charge unloaded, pull the solenoid coils off and stick a screw driver inside and then charge or take a wire off to deenergize unloader coils

  4. #4
    Join Date
    Sep 2002
    Posts
    1,389

    lodiroon

    Hook up your liq. line thermometer and then load the machine by over-riding the pressure switches long enough to take a reading when the thermometer restabilizes to a constant reading.

  5. #5
    Join Date
    Dec 2003
    Location
    Kenilworth New Jersey
    Posts
    230
    If they are the non electric pressure type unloaders you will need to energize the second circuit by overriding whatever controls that or adjust the unloaders themselves and set them up again when you`re done.