    Doing a remodel and installed a new split system. There is an existing split system twinned together (Heil). I need to install smoke detector in RA plenum in old units to bring up to code. No problem except they are not twinned together properly. I need to fix that problem before my detectors will work. I never twinned units before, but I know this was not done properly. Units do crazy things. detector is a Innovair dh100aacdclwp and want to insrall it using 24 volts.
    Thanks

  2. #2
    Join Date
    Oct 2003
    Location
    Michigan
    Posts
    727
    The PDF file on that detector does not show a wiring diagram but looks similar to ones I have used.
    Power the detector with 24v and then with the multiple contacts provided (N.C.) wire the control voltage power supply through the detector. If the smoke detector senses smoke it will open the control circuit to the units and shut them down.

    Oh yea Yooper are you from the U.P.????

  3. #3
    Join Date
    Jun 2001
    Location
    San Diego, CA
    Posts
    1,149
    You can use a Firex brand, but an invensys has an extra set of contacts, enough for both units.

  4. #4
    Join Date
    Aug 2004
    Posts
    15
    I don't have a problem wiring the detector, but the units aren't wired correctly together. Our main supplier is a heil dealer so I will just go there and get the proper kit. Thanks everyone.
    Ya a yooper but live in TN now. I try to get back to big snow country in the summer mostly now.

  5. #5
    Join Date
    Apr 2002
    Posts
    11,808
    Add a relay.

    I am guessing you have a normally closed contact on the detector.

    Put the 24V of the first unit through the contact and wire the first unit accordingly. Also tap off after the duct detector contact and power the coil of a relay. Control power from the first unit powers the relay coil as long as the duct detector is not in alarm.

    Wire the control voltage of the second unit through the normally open contact of this relay.
    The way we build has a greater impact on our comfort, energy consumption and IAQ than any HVAC system we install.

    http://www.ductstrap.com/

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event