    Anybody ever had a oil pump on 40-60 hp hemi hermetic recip have a " vapor lock" and not pump oil(0 psid). This occured on a replacement compressor on start-up. Compressor had proper oil charge.

    Never heard of it before but haven't fooled with recips for awhile.

  2. #2
    Join Date
    Jun 2002
    Posts
    48
    Post Likes
    Thread Starter
    Make that a "semi" hermetic. Got my soon to be new truck on my mind

  3. #3
    Join Date
    Jun 2004
    Location
    Richmond Virginia
    Posts
    1,078
    Post Likes
    There are a few compressors that have a one directional oil pump. That is, the rotation must be correct for the oil pump to pump anything. That's the only time I've seen what you are describing.

  4. #4
    Join Date
    Apr 2004
    Location
    Rossville, GA
    Posts
    105
    Post Likes
    Oil temperature is critical, cold oil kills positive displacement lubricated pumps pending application. Most compressor manufactors recommend that you prime the pump prior to start up or should i say it's a good procedure for such task. On the other hand i've seen many started up with no prime and run fine with good crankcase temp/press readings. I think 10 times on the discharge oil port is a good procedure with your oil pump. Vapor lock, what a sorry ass word.....And additionally don't buy a hemi when you can build stroker motor

  5. #5
    Join Date
    Mar 2003
    Posts
    1,877
    Post Likes
    proper oil charge has nothing to do with oil pressure anyway. unless you lower than the oil screen.

  6. #6
    Join Date
    May 2004
    Posts
    245
    Post Likes
    If this is a Copeland the oil pump is non directional. If the oil screen is not pluged and the pupmp is good it should pump. If it does not you can remove the plate on the face of the pump and remove the pump and inspect it to see if the drive is broken off of the gear. Be careful not to dislodge the pump body from the compressor body and you will not need gaskets. The pump cover is sealed with an o-ring that you should be able to reuse to reassemble. If it is broken and this is a new compressor get the wholesalehouse to give you a whole new compressor. Otherwise replace the oil pump. If the oil pump looks good but you still have 0 psi oil pressure get a new compressor. The crank is probably missing a plug where the oil passages are drilled. This HAS happened to me a couple of times.

    Good luck

  7. #7
    Join Date
    May 2004
    Posts
    7
    Post Likes

    oil pressure

    I learned along time ago to always pump oil into the oil pump on startup of a larger( 7 1/2 and up) it's just a good practice to get into. If the pressure doesn't come up and steady out it's time to return the replacement.
    Best Regards

  8. #8
    Join Date
    Jul 2004
    Posts
    8
    Post Likes
    If your having problems with oil pressure on start up - what were your procedures in starting? Is there refrigerant in the oil? What condition is the circuit in? Was proper clean up done? Did you gauge the oil pump on start up or after it threw the oil pressure cut out? Seems a lot more questions need to be asked before you throw out the "vapor lock" comment. However - Copeland does state this in their engineering bulletins and it is common occurance - go to the following web address: http://www.emersonclimatecontractor.com

    Register - it's free - then go to detailed product info, select publications search. Search for AE-1166-R10 and for AE-1182-R24. This will hold the answers to your "vapor lock" comment on Copeland oil pumps.


Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •