Thread: best way to clean icemakers
-
07-31-2004, 06:53 AM #1
Regular Guest
- Join Date
- Jun 2004
- Posts
- 160
I'm working on a scotsman icemaker and the tech's before me replaced all the controls with new controls (timer motor, finish relay)Originally posted by redwolf
If I haven't been servicing the machine usually the first thing I'll do is clean it.
but I've decided it's the liquid line solenoid stuck closed.
Unit runs fine in harvest but when freeze cycle starts unit pumps down and shuts off, same thing in harvest cycle when hot gas bypass wire removed from coil.
I'll have the solenoid and the filter/dryer in Monday.
My question is:
what is the best way to clean the resevoir and evaporator?
I found some calcium deposit on the evaporator and some sand in resevoir.
I'm just looking for the best general procedure, o yeah this is a scotsman model cms1002re.
ATDHVAANNKCSE..(thanks in advance)...
-
07-31-2004, 07:04 AM #2
Professional Member
- Join Date
- Apr 2001
- Location
- Camel City, NC
- Posts
- 6,221
cm scotsman
Use scotsman cleaner for machine. If your bin stat is bad, machine will pump down after defrost. Could have soldier joint on circuit board too. http://www.scotsman-ice.com/support/manualwelcome.pdf
[Edited by selfemployed on 07-31-2004 at 07:12 AM]Be safe not fast. body parts don't grow back
-
07-31-2004, 07:13 AM #3
Regular Guest
- Join Date
- Jun 2004
- Posts
- 160
i jumped out bin stat and unit still pumped down...
-
07-31-2004, 07:17 AM #4
Professional Member
- Join Date
- Apr 2001
- Location
- Camel City, NC
- Posts
- 6,221
CM
Did the scotsman site help? Look at the back of the board for bad connection.
Be safe not fast. body parts don't grow back
-
07-31-2004, 10:58 PM #5
Professional Member
- Join Date
- Aug 2002
- Posts
- 6,047
Ok, you jumped out the bin stat and the system still pumped down.Originally posted by kool it man
i jumped out bin stat and unit still pumped down...
Well ... is there proper voltage to the holding coil on the solenoid valve?
And I do mean CORRECT voltage!
If no, then you have to trace out where it stops.
If yes, then you need a coil, not the valve itself.
Have you downloaded the pdf from Snotsman?
-
08-01-2004, 03:34 AM #6
Regular Guest
- Join Date
- Jun 2004
- Posts
- 160
I 'm getting 208 volts to coil and I checked it with a clamp on amp meter at the coil and the solenoid looked good.
I did call the scotsman help line and they asked the same questions.
I even switched the hot gas solenoid with the liquid line solenoid and the same thing happened in the freeze cycle thet happened in the harvest cycle, so I'm satisfied the solenoid is bad not the coil.
It looked like the liquid line solenoid had been replaced
before as the pipe sizes didn't match
This is a real old machine but everything still looks like it works good..
-
08-02-2004, 04:46 PM #7
Regular Guest
- Join Date
- Jun 2004
- Location
- Long Island, NY
- Posts
- 37
Did you check to see if the coil is open. An open coil will give you a potential difference (Voltage reading)Indicating that the coil is good. Just a thought...
-
08-02-2004, 08:01 PM #8
Professional Member
- Join Date
- Apr 2001
- Location
- Camel City, NC
- Posts
- 6,221
kool it man
How bout an update.
Be safe not fast. body parts don't grow back
-
08-02-2004, 10:09 PM #9
Professional Member
- Join Date
- Aug 2001
- Posts
- 102
If your pressures are normal during harvest could be txv is not opening?
-
08-02-2004, 10:27 PM #10
Regular Guest
- Join Date
- Jun 2004
- Posts
- 160
Liguid line solenoid was not it, I feel like a hack replacing one part at a time.Originally posted by IceDoctorII
If your pressures are normal during harvest could be txv is not opening?
I replaced the solenoid and the filter dryer and the system still pumps down in freeze cycle.
looks like it is either the txv or could it be the capillary tubing after the txv?
what's the best way to tell...
or do I replace both the txv and the capillary tubing?