Results 1 to 6 of 6
Thread: CVHE
-
07-28-2004, 07:23 PM #1
Regular Guest
- Join Date
- May 2004
- Posts
- 17
Does anyone know why a CVHE050 black panel control would start having a problem when it loads to 91% start to unload to 30% then back to 91% over and over. Problem does not start until it loads to 91% or over. Unit is not controled by the computer and is ok wants the second chiller is online. Thanks
-
07-28-2004, 07:37 PM #2
Professional Member
- Join Date
- Aug 2000
- Location
- USA
- Posts
- 4,933
Sounds like the current calibrater needs to be adjusted to match FLA. I can email you a copy of the setup if you need it or you can order CTV-SB-22B.
[Edited by absrbrtek on 07-28-2004 at 07:41 PM]
-
07-28-2004, 07:43 PM #3
Professional Member
- Join Date
- Jun 2003
- Location
- in a tree looking in your window
- Posts
- 1,101
sounds like it could be running down to the low evap limit to me, have you checked the evap temp?
If you dont stand behind our troops, please feel free...........to stand in front of them.
-
07-28-2004, 08:08 PM #4
Regular Guest
- Join Date
- Sep 2000
- Location
- Miami, Fla. USA
- Posts
- 417
I Concur.Originally posted by chillrdude
sounds like it could be running down to the low evap limit to me, have you checked the evap temp?
-
07-28-2004, 08:10 PM #5
Professional Member
- Join Date
- Aug 2000
- Location
- USA
- Posts
- 4,933
Me too now that I "thought" about it.
Originally posted by Chomper
I Concur.Originally posted by chillrdude
sounds like it could be running down to the low evap limit to me, have you checked the evap temp?
-
07-28-2004, 09:16 PM #6
Regular Guest
- Join Date
- May 2004
- Posts
- 17
I have not been to the job yet, just got the service call and will be there tomorrow. Thanks