    Trane RTAC suction butterfly valve

    We have found many of these leaking...dumping the entire charge. All on RTAC units and all on units less than 3 years old. Mostly finding them leaking thru the stem but twice found leaking at flange. I heard from a Trane guy about putting washers on the flange bolts because they found on some the bolts were bottomed out. But finding several leaking thru stem is raising an eyebrow. Anyone else finding this or know of a service bulletin?

  2. #2
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    3,600
    Post Likes
    2 of our 6 newer RTAC's have had this problem and trane had to come out and fix them in warranty.

  3. #3
    Join Date
    Jul 2001
    Location
    maryland
    Posts
    1,412
    Post Likes
    Yes there is a problem and that's about as much as you'll get out of me. Maybe some of the others will be more forthcoming.

  4. #4
    Join Date
    Feb 2008
    Location
    Pensacola Florida
    Posts
    33
    Post Likes
    Thread Starter

    Cool

    Quote Originally Posted by mallron View Post
    Yes there is a problem and that's about as much as you'll get out of me. Maybe some of the others will be more forthcoming.
    well, by the lack of response I can tell it must be "hush hush" confidential service bulletin.

    its cool. i get it.

    thanks )

  5. #5
    Join Date
    Jan 2004
    Location
    Oregon
    Posts
    2,096
    Post Likes
    Funny, I have never found a leak there.

  6. #6
    Join Date
    Aug 2007
    Location
    Central Texas
    Posts
    118
    Post Likes

    RTAC

    I have replace "many" butterfly valves!

  7. #7
    Join Date
    Mar 2007
    Posts
    3,824
    Post Likes
    I've never had to replace any so far, and haven't seen any leaks at the stem either.
    Don't pick the fly crap out of the pepper.

  8. #8
    Join Date
    Jun 2010
    Location
    U.A. (upper Alabama)
    Posts
    1,253
    Post Likes
    I have heard many techs say to check B.F. valves first if you are low and every time I done it was in vane, all the leaks i've seen on rtac's were on threads on u name it 1/4" plugs, reliefs, and press. tranducers. I hope they've changed they're thread sealant and stopped Sally from having to tighten all of them. lol

  9. #9
    Join Date
    Dec 2006
    Location
    Massachusetts
    Posts
    29
    Post Likes
    i have had a few. yes check the bolts for bottoming out. stem leaks...yes they leak... sometimes....sometimes they don't

  10. #10
    Join Date
    Sep 2006
    Posts
    86
    Post Likes
    They went to a new setup now they are using a cap with an o-ring over the valve stem to prevent leaks

  11. #11
    Join Date
    Jul 2010
    Posts
    15
    Post Likes
    Never had a leak at the butterfly but have changed many factory charging valves (on the barrel close to BF) in our environment these steel valves fall apart in 3 years I now change them with parts from the hardware store Mhose X 3/8fpt and a 3/8 service valve from the supply house/

  12. #12
    Join Date
    Sep 2006
    Posts
    86
    Post Likes
    Floridaactecdj do you have any pictures of this valve in stainless steal from hardware store ?

  13. #13
    Join Date
    Nov 2007
    Location
    Mississippi
    Posts
    1,571
    Post Likes
    I have found two in the last week. One was on the stem and the other was around the flange. Both units were 2008 models.

  14. #14
    Join Date
    Jan 2009
    Location
    Tampa
    Posts
    1,467
    Post Likes

    its on there

    i found the (general service bulletin) on the Step by Step repair of what you are looking for, It is on the Comfortsite., good bulletin
    no signature blast'em man blast'em
    !!!KILL THE TERRORIST!!!

  15. #15
    Join Date
    Jan 2012
    Location
    Perth Down Under
    Posts
    26
    Post Likes
    I have enever had this problem down under but from a logically point of view, if the bolts are to long, replace them or add washers, if from the seals, run the compressor at full load and while doing this move the valve. Being any oil enriched system oil may enter the seals providing the seal required or just replace the valve.

  16. #16
    Join Date
    Dec 2010
    Location
    west virginia
    Posts
    18
    Post Likes
    Just changed a valve on a 2010 machine. Leaking from the stem, this is the first one our of 4 that gave any probelems. The cap worked out nice

  17. #17
    Join Date
    Oct 2011
    Posts
    2
    Post Likes
    just worked on a RTAC chiller about a month ago. Found circuit completely flat on charge. All 225# gone. Found it leaking around the entire flange. I heard from someone I know from Trane that they are having a lot of problems with this. It will come out on a service bulletin soon. Makes me wonder if the Poloyl oil is eating it up

  18. #18
    Join Date
    Nov 2005
    Location
    Missouri
    Posts
    34
    Post Likes
    I have had to replace the butterfly assembly due to a leak. http://hvac-talk.com/vbb/showthread.php?t=986651

  19. #19
    Join Date
    Sep 2005
    Location
    Pa
    Posts
    305
    Post Likes
    I got on this site today with the intention of asking about this very subject. Found a stem leaking today, wondering what the repair would be , replace the valve or repack the stem if possible. Thats a tough thing to have to tell the customer after making the repair that you have to add 175# of gas!! This chiller is approx 2008 vintage.
    I caught wind of the problem with the flange bolts last year, thats what I expected to find when I saw the "low evap. temp. diagnostic. Nope, it was the stem.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •