    Field Piece Air Velocity Head

    I bouth the head for the AAV3 Air Velosity head and question their explanation of calcuating the CFM they state to take the free area of the register and x that by length and width devide by 12 to get the Cft and take the average Feet per min mesuerment to get CFm. There had to be a better way, or am I way confused on this one? also what is the break down to btu output and tonnage in regards to each registers cfm. Not sure if I can post here with this question , just checking.

    Thanks,

    Ken Atcher Service,

    bty if your on a budget for comfortech, I got a room across the street from the convention for $80 a night at the days in, looks like a good room. Hotel .com for rates

  2. #2
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    62,215
    They mean to measure the area where the louvers are to find its area. You should then convert that to sq ft.

    The area you measure though. is not the actual free area. Since it has louvers. Many supply registers are only 70% free area.

    sq ft time FPM equals CFM.

    Go to Hart&Cooley's website. They have a lot of usefull info you can down load. On check air flow at registers and grilles.
    Contractor locator map

    How many times must one fix something before it is fixed?

  3. #3
    Join Date
    May 2010
    Location
    Las Vegas
    Posts
    52
    Been There,

    Thanks for the advice will check it out.

  4. #4
    Join Date
    Nov 2004
    Location
    NJ
    Posts
    1,165
    Ken, do you live in Vegas?
    Ed J

  5. #5
    Join Date
    May 2010
    Location
    Las Vegas
    Posts
    52
    Yes..do u

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •