Results 1 to 8 of 8
    Nov 2001
    East Texas
    Need to replace cond. unit.
    Comp was replaced about 5 years ago. It is a copeland
    JRL4-0500-IAA-958
    The evap has a pump that pumps the condensate up to a pan on top. There is a coil of copper tubing in the pan that the hot gas flows thru before it goes to the air cooled condenser.
    What cond unit should I use for replacement?
    Anybody have exp. with this puppy?
    Nov 2001
    East Texas
    Mccall
    Model: 4001 RT
    Serial: M289 74
    Medford Oregon
    the unit in that case is Copelans's CopeEvap unit, used in self contained units that have minimum condensor or poor airflow. A standard unit will usually go off on high head. Get the Copeland unit model (probably FBEH-0050) and go to your Copeland distributor and get cuurent CopeEvap model. Usually not stocked, so be prepared to wait. Or you can just change commpressor which won't be an axact fit.
    Nov 2001
    East Texas
    United refrigeration reccomends a MBFH-0050-IAA-109
    Will this work with the original evap?
    Medford Oregon
    MBFH-0050-IAA not a CopeEvap unit, will probably not work
    the "E" as 3rd letter represents CopeEvap
    they are probably reccommending that based on nominal HP and don't know what CopeEvap is
    if your unit was an FBEH-0050-IAA then Copeland suggest an M2EM-0048-IAA R134a unit (can use MP39 if desired)
    Nov 2001
    East Texas
    Mccall says they are 90% sure that the original cond unit was a FBAM-A050-IAA
    What does this cross to?
    Medford Oregon
    the FBAH-0050-IAA crosses to MBFH-0050-IAA
    the FBAH did not have facitities for coppper tube in drain pan so double check with with manufacturer. if it really was an FBAH the the MBFH will do fine
    Nov 2001
    East Texas
    what do u mean by facilities
    Are ther cut sheets on these 2 diff. models?
    If i use the MBFH can I just pipe in the hot gas coil that goes to the drain pan?