questions on piping for air drier compressor is out on thermal overload, hot gas bypass regulator does not have solenoid valve before or after
-
07-23-2004, 09:20 PM #2
Regular Guest
- Join Date
- Nov 2002
- Posts
- 45
What is your question???? If i am guessing right your unit is low on gas..... Look for leak. They use the hot gas to control the load.
-
07-23-2004, 11:09 PM #3
Member
- Join Date
- Mar 2003
- Posts
- 1,877
hotgas valve should not begin to open to pressure drops to 58 lbs. what is you subcooling and superheat. is your compressor hot. do you have adequate charge are coils clean.
what is subcoolingand superheat.
you will never get a right answer without subcooling and superheat. you will never get a correct answere without subcoooooooooooollllllllllling and superhhhhhhhhheeeeeeeaaaaaaaaaaattttttttttttt.
-
07-23-2004, 11:11 PM #4
Professional Member
- Join Date
- Oct 2003
- Posts
- 566
You make a subtle point...Originally posted by airworx
what is subcoolingand superheat.
you will never get a right answer without subcooling and superheat. you will never get a correct answere without subcoooooooooooollllllllllling and superhhhhhhhhheeeeeeeaaaaaaaaaaattttttttttttt.
-
07-24-2004, 11:33 AM #5
Worked on an air drier several months back that had a bad txv power head. Hot gas valve was keeping suction pressure up, but suction line was HOT! Removed charge and looked for a leak, only to find a tight system. Backed off the bypass valve setting to keep the valve closed, and the suction side went to a vacuum. Replaced power head, and reset bt-pass valve.
-
07-24-2004, 02:15 PM #6
Member - bad email, contact Admin
- Join Date
- Sep 2002
- Posts
- 1,389
airworx reply:
That about says it all.