    Good morning. I have a fireproof vault that's about 190 square feet with an 8 to 9 foot ceiling. How can I provide air conditioning (no heat) to this room with an independent unit/system set outside of this room and still maintain a fire rating?

    Any ideas would be greatly appreciated!

    Thanks!

    Thank you for your time! ~KMT

  2. #2
    Join Date
    Jul 2000
    Location
    Dallas,Texas
    Posts
    4,804
    Fire dampers in the duct at wall and cieling penetrations.

  3. #3
    A ductless split system could also be a very viable solution for minimum penetrations.

  4. #4
    Join Date
    Sep 2002
    Location
    Hampton Roads, Virginia
    Posts
    1,463
    Originally posted by maintmankc
    A ductless split system could also be a very viable solution for minimum penetrations.
    They probably will not allow any electrical system in vault.
    "Profit is not the legitimate purpose of business. The legitimate purpose of business is to provide a product or service that people need and do it so well that it's profitable."

    James Rouse

  5. #5
    DOH.....good point

  6. #6
    Join Date
    Apr 2002
    Posts
    11,808
    Originally posted by maintmankc
    A ductless split system could also be a very viable solution for minimum penetrations.
    depending on the fire rating you may have to put donuts to squsih the armaflex in case of a fire. Sounds funny but I have seen this requested by building officials.
    The way we build has a greater impact on our comfort, energy consumption and IAQ than any HVAC system we install.

    http://www.ductstrap.com/

  7. #7
    Join Date
    Oct 2002
    Posts
    970
    Originally posted by wolfdog
    Fire dampers in the duct at wall and cieling penetrations.
    Yes, but also put high quality duct dampers outside the room with Belimo actuators (spring return) on supply and return with auxillary swithes for fire panel interlocks to kill the unit in alarm conditions.
    I work with the Chiller Whisperer...