    Hmm retrofitting 410 handler to run on 22

    I have a bad inside coil on a R22 3 ton rooftop heat pump. The customer wants to only replace the handler and does not want to spring for a new matched system.
    Can a new R410 coil for inside be retrofitted to run on 22, Has anybody successfully done this without royal pain??

  2. #2
    Join Date
    Apr 2010
    Location
    SLC,Utah
    Posts
    35
    Rooftop Heatpump, matched system?

    I am confused, is this a rooftop system or a split system?

    If it is a split system then you should still be able to get an evap coil for it.
    If it is a rooftop contained system then you should replace with exact manufacturer coil in my opinion.

    You can even have a coil made by a contractor like Coil Company, Darby-Colwyn, PA 19023.

  3. #3
    Join Date
    Jan 2008
    Location
    Dallas ,Texas
    Posts
    3,511
    I will say that it can be done . As long as you put a 22 TXV on it you will be ok. I took a R-22 coil And turned it into a 410A system. But I wasn't worried about any ratings since this was for my home.
    UA 100

    It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.

  4. #4
    Join Date
    Feb 2008
    Location
    Milton Florida
    Posts
    33
    like good listener mentioned.....just change the txv(r22) to match that condenser and you will be fine

  5. #5
    Join Date
    Jun 2007
    Location
    Laytonsville MD
    Posts
    8
    This is split unit-condenser on roof- not package wmagnin, Thanks Boys I 'll go ahead and put 22 txv on the Evap coil. 22 coils harder to get now!