Results 1 to 4 of 4
  1. #1
    Join Date
    Apr 2003
    Location
    South Carolina
    Posts
    82
    Post Likes
    I have a RTHB150 that is carrying over at 48% load. Machine runs fine above and below this %.

  2. #2
    Join Date
    Aug 2000
    Location
    Under my tree
    Posts
    5,086
    Post Likes
    Has oil been added to the unit lately? Are the evaporator tubes clean? Has refrigerant been added to the unit? Is the EEV working properly?

  3. #3
    Join Date
    Apr 2003
    Location
    South Carolina
    Posts
    82
    Post Likes
    Thread Starter
    once loaded had a 4deg approach. Pressures normal, Compressor discharge temp was low and discharge superheat was low but all corrected when machine loaded

  4. #4
    Join Date
    Jun 2003
    Location
    in a tree looking in your window
    Posts
    1,350
    Post Likes
    When the discharge temp was low and the discharge superheat was low, what was the expansion valve doing and what was it's position. Was it running in extended unloading?
    If you dont stand behind our troops, please feel free...........to stand in front of them.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.