    I have a RTHB150 that is carrying over at 48% load. Machine runs fine above and below this %.

  2. #2
    Join Date
    Aug 2000
    Location
    USA
    Posts
    4,958
    Has oil been added to the unit lately? Are the evaporator tubes clean? Has refrigerant been added to the unit? Is the EEV working properly?

  3. #3
    Join Date
    Apr 2003
    Location
    California
    Posts
    82
    once loaded had a 4deg approach. Pressures normal, Compressor discharge temp was low and discharge superheat was low but all corrected when machine loaded

  4. #4
    Join Date
    Jun 2003
    Location
    in a tree looking in your window
    Posts
    1,101
    When the discharge temp was low and the discharge superheat was low, what was the expansion valve doing and what was it's position. Was it running in extended unloading?