I have a RTHB150 that is carrying over at 48% load. Machine runs fine above and below this %.
-
07-21-2004, 10:03 PM #2
Professional Member
- Join Date
- Aug 2000
- Location
- USA
- Posts
- 4,933
Has oil been added to the unit lately? Are the evaporator tubes clean? Has refrigerant been added to the unit? Is the EEV working properly?
-
07-21-2004, 10:16 PM #3
once loaded had a 4deg approach. Pressures normal, Compressor discharge temp was low and discharge superheat was low but all corrected when machine loaded
-
07-21-2004, 10:38 PM #4
Professional Member
- Join Date
- Jun 2003
- Location
- in a tree looking in your window
- Posts
- 1,101
When the discharge temp was low and the discharge superheat was low, what was the expansion valve doing and what was it's position. Was it running in extended unloading?