    DX-9100 Question

    I replaced 2 Velocity Pressure Sensors and had problems with the readouts being accurate. I then converted each sensor's AI from 4-20Ma to 0-10Volt by removing the AI jumpers on the back of the DX-9100, and re-configuring each AI's configuration in GX9100.
    BTW, I used the DX Commissioning App to verify live values after creating a DMO file in GX9100.
    Anybody think of anything I might have missed?
    Jogas
    Four wheel therapy, my 1968 Camaro

  2. #2
    Join Date
    Sep 2008
    Location
    Houston and Katy
    Posts
    74
    1. You removed the jumper from the current block and installed it on the 0-10 voltage block?
    2. Did you bump up the filter constant time (seconds)?

  3. #3
    Join Date
    Jun 2005
    Location
    Ohio
    Posts
    1,691
    Quote Originally Posted by rellufnalla View Post
    1. You removed the jumper from the current block and installed it on the 0-10 voltage block?
    2. Did you bump up the filter constant time (seconds)?
    Yes.
    Both sensors now work, but the readout in DX Commissioning and the DX9100 are still reading high.
    If Return Vp actually equals 0.663, the readouts and display says 1.4.
    If Supply Vp actually equals 0.845, the readout and display says 1.8.
    I have both sensors set up as 0-5 IWC = 0-10VDC
    I have both AI's set up as: Low Value/Limit = 0
    Hi Value/Limit = 5
    Any ideas?
    Jogas
    Four wheel therapy, my 1968 Camaro

  4. #4
    Join Date
    Sep 2008
    Location
    Houston and Katy
    Posts
    74
    Quote Originally Posted by jogas View Post
    Yes.
    Both sensors now work, but the readout in DX Commissioning and the DX9100 are still reading high.
    If Return Vp actually equals 0.663, the readouts and display says 1.4.
    If Supply Vp actually equals 0.845, the readout and display says 1.8.
    I have both sensors set up as 0-5 IWC = 0-10VDC
    I have both AI's set up as: Low Value/Limit = 0
    Hi Value/Limit = 5
    Any ideas?
    If it is double the value for the entire scale you need, then change your range to 10 inches from 5 inches. Reading the feedback with a voltmeter, are you showing 2 volts dc for 1 inch of static? If not, maybe your sensors were mislabeled or calibrated wrong.

    Last question - are you doing two wire or four wire? Two wire voltage wiring requires a jumper at the dx to power the circuit.

  5. #5
    Join Date
    Jun 2005
    Location
    Ohio
    Posts
    1,691
    Quote Originally Posted by rellufnalla View Post
    If it is double the value for the entire scale you need, then change your range to 10 inches from 5 inches. Reading the feedback with a voltmeter, are you showing 2 volts dc for 1 inch of static? If not, maybe your sensors were mislabeled or calibrated wrong.

    Last question - are you doing two wire or four wire? Two wire voltage wiring requires a jumper at the dx to power the circuit.
    That's the weird thing. The Voltage agrees with a 0-5 IWC scale.
    Sensors are 4-wire using 24VAC.
    And I did change the jumpers in back of the DX9100 and relocated the sensor wires to the AI and Common terminals (the sensors were originally 4-20 Ma and were wired to the 15VDC Terminal).
    Jogas
    Four wheel therapy, my 1968 Camaro

  6. #6
    Join Date
    Sep 2008
    Location
    Houston and Katy
    Posts
    74
    Quote Originally Posted by jogas View Post
    That's the weird thing. The Voltage agrees with a 0-5 IWC scale.
    Sensors are 4-wire using 24VAC.
    And I did change the jumpers in back of the DX9100 and relocated the sensor wires to the AI and Common terminals (the sensors were originally 4-20 Ma and were wired to the 15VDC Terminal).
    Then I would say your point configuration is not actually setting the value in the controller - even though it says it is when you look at it on the GX, display or front end. I would wipe the program out (download a blank program) and reload it with your program.

    Or try doubling the range to 10 inches and see what happens.

  7. #7
    Join Date
    Jun 2005
    Location
    Ohio
    Posts
    1,691
    Quote Originally Posted by rellufnalla View Post
    Then I would say your point configuration is not actually setting the value in the controller - even though it says it is when you look at it on the GX, display or front end. I would wipe the program out (download a blank program) and reload it with your program.

    Or try doubling the range to 10 inches and see what happens.
    Will do...thanks.
    Jogas
    Four wheel therapy, my 1968 Camaro