    I have noticed some companies using a different sensor to replace failed CPC sensors. There is no name or markings on them. A friend of mine says his company starting using them because they are a 1/3 of the price of CPC, but has no idea where they are getting them from.
    Anybody have any idea who makes them and if you have used them, have you had sucess with them.

  2. #2
    Join Date
    Jul 2006
    Location
    Washington
    Posts
    285
    Post Likes
    juneair,
    what is a cpc sensor.
    I'm trying to soak up as much as I can.
    I'm a typical hvac tech that gets more thrown at him than one knows.
    Learning everyday so please be easy on me
    Thanks for your educational responce

  3. #3
    Join Date
    Jan 2006
    Location
    DFW Metroplex
    Posts
    4,910
    Post Likes
    Originally posted by travistee
    juneair,
    what is a cpc sensor.
    I'm trying to soak up as much as I can.
    I'm a typical hvac tech that gets more thrown at him than one knows.
    Learning everyday so please be easy on me
    Thanks for your educational responce
    CPC stands for Computer Process Controls. This is a company that manufactures computers if you will that can control several aspects of any HVACR system.

    A sensor is a device that measures temperature. Whether it be discharge air, discharge line, suction line, outside ambient, etc...........

    Juneair - We did not get involved in ordering our own parts - sorry, unable to help.

  4. #4
    Join Date
    Aug 2002
    Location
    Orange County CA
    Posts
    1,084
    Post Likes
    We use them

    They have grey leads and they work great.

    Sorry don't know the maker though.


  5. #5
    Join Date
    Feb 2003
    Posts
    1,173
    Post Likes
    The CPC sensor is a common 10K ohm sensor, we used a compatible sensor made by Basys Controls, Middleton Wisconsin, ph.(608)836-9034. fax. (608) 836-9044
    I happened to have 1 sitting in the kitchen drawer for the last 5 years unopened, hence the detailed info. They worked fine initially but did not have the same life expectancy as a CPC sensor. Don't have time to supply a picture but they do not appear to be sealed as well where the wire leads meet the sensor (can't tell due to wire spring on sensor, could likely be helped by a few wraps of tape or heat shrink to keep out moisture)
    They were cheaper but some had to replaced within 1 year or less!! They did generate more income because of that but....could piss of a customer with that kind of failure rate.

    There are likely a lot of companies that make 10k ohm sensors,you can swap 1 for your Cooper electro therm sensor if you can solder together the right connector/plug-in.
    Watts New, Ohm My, I been Electrically Commutated. Are U2.

  6. #6
    Join Date
    Nov 2003
    Posts
    1,867
    Post Likes
    We use some with yellow leads, don't know mfg.
    I still like green.

  7. #7
    Join Date
    Dec 2004
    Location
    Sunny So Cal!
    Posts
    649
    Post Likes
    Originally posted by mccool
    The CPC sensor is a common 10K ohm sensor, we used a compatible sensor made by Basys Controls, Middleton Wisconsin, ph.(608)836-9034. fax. (608) 836-9044
    I happened to have 1 sitting in the kitchen drawer for the last 5 years unopened, hence the detailed info. They worked fine initially but did not have the same life expectancy as a CPC sensor. Don't have time to supply a picture but they do not appear to be sealed as well where the wire leads meet the sensor (can't tell due to wire spring on sensor, could likely be helped by a few wraps of tape or heat shrink to keep out moisture)
    They were cheaper but some had to replaced within 1 year or less!! They did generate more income because of that but....could piss of a customer with that kind of failure rate.

    There are likely a lot of companies that make 10k ohm sensors,you can swap 1 for your Cooper electro therm sensor if you can solder together the right connector/plug-in.
    Geez Mccool clean out yer drawers fr petes sake....
    Look, just do your job, stay outta my way and we'll get along fine.

    Teach your kids to respect themselves and others with your actions- these little baboons will imitate you like it or not.

  8. #8
    Join Date
    Aug 2006
    Location
    Wisconsin
    Posts
    26
    Post Likes

    ACI Sensors

    Try Automation Components (ACI). They have green lead versions to match the look of the CPC sensors....
    Enjoy your day!

  9. #9
    Join Date
    Dec 2006
    Location
    In a Mess
    Posts
    1,087
    Post Likes
    I've used 3 different Green lead type, not sure where they all come from but they're different makers. I also have a few with orange leads, there's a flat/curved spot on the sensor which makes mounting it to a pipe better. kinda like the curved spot on some danfoss TEV bulbs.
    Mike
    Sig removed by mod. G-Rated site

  10. #10
    Join Date
    Apr 2007
    Location
    Loris SC
    Posts
    208
    Post Likes
    CPC sensor to a Danfoss Sensor to a Novar Sensor To A Comtrol Sensor, If you dont know the differerance then there's something wrong

  11. #11
    Join Date
    Dec 2006
    Location
    In a Mess
    Posts
    1,087
    Post Likes
    Quote Originally Posted by refertecbd View Post
    CPC sensor to a Danfoss Sensor to a Novar Sensor To A Comtrol Sensor, If you dont know the differerance then there's something wrong
    a 10K resistor is a 10K resistor

    no experience with comtrol, danfoss and Novar, what do they use

    CPC and Microthermo are OK with the 10K ohm puppy
    Sig removed by mod. G-Rated site

  12. #12
    Join Date
    Nov 2006
    Location
    Mirabel, QC, Canada
    Posts
    88
    Post Likes
    Quote Originally Posted by MikeySq View Post
    a 10K resistor is a 10K resistor

    no experience with comtrol, danfoss and Novar, what do they use

    CPC and Microthermo are OK with the 10K ohm puppy

    Sensors are 10K thermistors, not resistors. There is a "10K Type 2", and a "10K Type 3". As you may know, thermistors are non-linear devices. A change of x ohms in the measured resistance does not always correspond to a change of y degrees. It depends where on the range of the device you are.

    Most controllers have a built-in idea of the curve for "10K type 2" and/or "10K type 3". Which is why they can give an accurate temperature reading even if thermistors are not linear.

    Type 2 and Type 3 do not have exactly the same curve. If the application requires precision, you need to use the right type. If in doubt, ask the manufacturer what 10K type is supported by their controllers.
    -------------------------
    CO2 Racks Rock !

  13. #13
    Join Date
    Apr 2007
    Location
    Loris SC
    Posts
    208
    Post Likes
    !!!! Resistor !!! not resistor!!! maybe resistacne has a value??

  14. #14
    Join Date
    Nov 2006
    Location
    Mirabel, QC, Canada
    Posts
    88
    Post Likes
    Quote Originally Posted by juneair View Post
    I have noticed some companies using a different sensor to replace failed CPC sensors. There is no name or markings on them. A friend of mine says his company starting using them because they are a 1/3 of the price of CPC, but has no idea where they are getting them from.
    Anybody have any idea who makes them and if you have used them, have you had sucess with them.
    Hello juneair,

    My company (Micro Thermo Technologies) sells "compatible CPC sensors" to integrators, refrigeration companies, hvac companies, OEMs, and directly to the end user. Can't comment about the price. Not my departement. Just call Patrick Desmarais at (450) 668-3033 (extension 119) 9am-5pm, mon-fri, eastern standard time.

    Regards,
    -------------------------
    CO2 Racks Rock !

  15. #15
    Join Date
    May 2008
    Location
    Collinsville, Tx (Texoma)
    Posts
    53
    Post Likes
    Quote Originally Posted by MikeySq View Post
    I've used 3 different Green lead type, not sure where they all come from but they're different makers. I also have a few with orange leads, there's a flat/curved spot on the sensor which makes mounting it to a pipe better. kinda like the curved spot on some danfoss TEV bulbs.
    Mike
    I believe the sensor you have with the curved spot is a CPC sensor. They use them to take Hotgas temperatures at the compressors

  16. #16
    Join Date
    Dec 2006
    Location
    In a Mess
    Posts
    1,087
    Post Likes
    Quote Originally Posted by Keep'N It Cool View Post
    I believe the sensor you have with the curved spot is a CPC sensor. They use them to take Hotgas temperatures at the compressors
    we use them for defrost termination senors clamped to the hot gas return line
    Sig removed by mod. G-Rated site

  17. #17
    Join Date
    May 2008
    Location
    Collinsville, Tx (Texoma)
    Posts
    53
    Post Likes
    Yes they are also used for that in conjunction with a "POS TD3" or a Contol Link Modual.

  18. #18
    Join Date
    Jun 2010
    Posts
    1
    Post Likes
    There's a company in Canada www.recs.ca who supplies equivalents to CPC sensors, the green ones and orange for defrost termination. They work great, I've tried them and they cost much less.
    Last edited by Bazooga; 06-10-2010 at 05:00 PM. Reason: spelling

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •