Results 1 to 13 of 23
    this unit im workin on, charged wit r-22, has a suc pressure of 90 and a head pressure of 245... super heat is 5 degrees and im not sure what the sub cool is cuz it has a water cooled condenser coil and that just threw me off..at first i thought it was undercharged but then i thought well the super heat low and the suc pressure is really high so maybe thats not it....the system has been operating for bout 15 yrs and filters have been changed on time but the evap coil is filthy and has NEVER been cleaned......can a dirty coil cause high suc pressure?
    OOPS, your right.High load will cause high suction pressures too.
    [Edited by acjourneyman on 07-19-2004 at 12:56 AM]
    Nov 2001
    California
    The only way a dirty coil will cause high suction is if it's the condenser coil that's dirty.
    If you want help troubleshooting this problem, we need a lot more info. Get every piece of info you can think of and post it. You should get plenty of offers for help then. We can only guess if we don't know more of what's happening with the system, and if we guess, we may send you down the wrong path.
    What kind of unit...package air conditioner, wine cooler, split system heat pump??? What brand, size and/or model#?
    return air temp, supply air temp, entering condenser water temp, leaving condenser water temp, receiver?, sight glass?, TXV?, length and diameter of refrigerant lines, refrigerant lines insulated?, do the lines go through a hot attic or through a cold room, etc.
    Don't let a water cooled condenser keep you from taking subcooling. Subcooling is nothing other than the amount of temperature difference between the saturated temp of the liquid refrigerant in the condenser, and the measured temp of the liquid line. If 245 psig is the pressure at the liquid line service valve (not the compressor discharge service valve) look at your gauge or PT chart and see what the saturated temp is at that pressure. Then subtract the measured temp of the liquid line from that reading to obtain subcooling.
    Dec 2003
    you can also check the td through the water coil for more info.
    there but for the grace of god, go all of us
    midlands of the uk
    we had this situation with the water chillers we cleaned the coils but still had problems.
    Turned out that the condensing fans four in total were not correctly set up on the hp pressure switch used to bring them on fans no2 and 3 were set to close together and quickly bought down the head pressure to quickly
    so clean those coils and check the fans to see if they are pressure controlled or varable speed
    good luck
    a speeding slug is a snail with out a home
    Virginia
    What's the load in the space trying to be cooled?What is your compressor amp draw?
    KISS
    Clean that evap coil.
    Make sure you got the airflow you need across your evap coil.
    THEN ..... then take some pressure readings and temps.
    What your telling me is you got a 95 degree room. This is from your low side reading.
    You hi side reading could be ok. It is a little hi right now, but just look at the load on the system.
    Once you get her all cleaned up .... things will change and you can then make a better diagnosis. Right now you cannot do that.
    Red Lion, PA
    Talking
    i agree with LEARNER i think people are to quick to give advice without all of the information its tough to give good advice for those of you who think im wrong lets use this problem some one writes ive got 18 deg superheat and 9deg subcooling and my temp split is 4 deg whats wrong? well maybe nothing if its a flower box with a low e coil! you can guess all day but the more info you have the better these people can serve your needs how come nobody lists discharge temp? condenser split what temp unit is ment to maintain? and for heavens sake if a coil is dirty clean it first ! if a condenser cant condense how can you get liquid? this is a big problem in captube systems well im done rambling for now
    yea i only work at this hotel part time...that is where the unit is located....i just got my epa so my boss lets me fool around wit the systems to get familiar with them for when i finish school, so any ways yea ill get more info when i go back to work on thurs and ill post it up.. only other thing i can pretty much say is that its a heat pump, package unit stored in the ceiling of a hotel ballroom covered by ceiling tile so its VERY difficult to work on with all the duc work and pipes running around and pretty much theres no space. oh yea and it has capillary tube and the entering water temp for the condenser is 82 degrees F.
    thanx guys!
    Nov 2001
    California
    Cool
    OK, and you have a cap tube system and cond ent wtr temp of 82 degrees. You've just given us some hints as to what's wrong. But don't just accept it at face value. Put your thinking cap on, as much as possible for a new technician beginning to learn the trade.
    245 psi on the high side is what temp according to your temperature/pressure P/T chart? I think it's over 115 degrees. Now, that is EXCESSIVE for 82* Cond Ent Wtr Temp. Generally speaking, most water cooled condensers have about a 10 degree split.
    OK, now think about this next part...many journeyman haven't figured this one out yet, so get a step ahead of them. You have a cap tube system. A cap tube is a "fixed orifice" type of metering device (not modulating like an expansion valve). With a fixed orifice, the higher the refrigerant pressure entering the metering device, the more refrigerant will be metered through it. Now, if you have more refrigerant going through, and into the evaporator, the LESS superheat you will have, because you are OVERFEEDING if the high side pressure is excessive.
    What causes high head pressure??? Things like overcharge of refrigerant (my guess in your case), dirty (fouled) condenser, lack of condenser water flow, air in the system, and probably a few other things.
    By the way, high head pressure typically causes high suction pressure, especially on a cap tube (fixed orifice) system.
    More information could cause me to modify my advise, however, based on what you've told us, here's my recommendation.
    1. Even though this is not the cause of high suction, Clean The Evaporator, because it needs to be clean. If it's dirty, it causes LOW suction pressure, and causes inexperienced techs to overcharge a system.
    2. Just for kicks, and for a learning experience, check the system vitals, and record the pressures, water temp entering and leaving the condenser, air temp entering and leaving the evaporator, measure superheat, and subcooling.
    3. Make the needed repair: Recover all of the refrigerant (weigh it so you can see how much it was overcharged). Pull a vacuum, and weigh in the correct refrigerant charge per the data tag.
    4. Take the system vitals again, recording the temps and pressures, and go to your boss with a smile because you've gained some valuable experience, and you've fixed his equipment.
    need subcooling for correct diagnosis. liquid line is a liquid line. water or cooled doesnt matter. 5 degrees is to cold unless this is a flotronic chiller. head pressure on a watercooled unit should not be over 225 or scaling will increase. pull the ends off brush the tubes. pull and clean orfices in tower then clean strainer and tower basin. you should run 10 degrees subcooling and 15 to 20 degrees superheat. unless this is a flotronic. then you would run 29 degrees superheat across windings or 3 to 10 degrees superheat depending on eprom chip. subcooling will depend on exv percent open.
    Nov 2001
    California
    ... its a heat pump, package unit stored in the ceiling of a hotel ballroom covered by ceiling tile ... and it has capillary tube ...
    Red Lion, PA
    IM BETTING ITS A COAXIAL COIL CANT CLEAN IT THAT WAY