    Question

    compression ratio..can you give some info about it.things that I don`t find in books.would you get any help from it to diagnose anything?

  2. #2
    Join Date
    Sep 2002
    Location
    South Dakota
    Posts
    6,580
    Post Likes

    Calculating compression ratio is of little value to the service technician on the job. The compression ratio changes very little with changes in pressures that occur in the field. You will have major problems long before the compression ratio indicates there is a problem.

    Volumetric efficiency is a better indicator of a problem but that is not possible to calculate. You need the capacity charts for your particular compressor to determine the volumetric efficiency.

  3. #3
    Join Date
    Nov 2003
    Location
    Greater Toronto Area - Canada
    Posts
    40
    Post Likes
    We actually do use compression ratio as a troubleshooting tool on ultra low cascade compresors. The compression ratio should be at least 11:1. If not, the compressor capacity is diminished enough that we won't make temperature. This is on a Copeland 1 HP Hermetic.
    When a system won't quite make -85 deg.C, you are looking at a partial restriction (usualy oil logging), refrigerant leak, or weak compresor (leaking valves). this is just one more tool to help determine which one is the problem. The refrigerant charge is quite small by volume and very critical.
    To calculate, you need to take your absolute Discharge pressure and divide by your absolute suction pressure. The answer is expressed as a ratio to "1". PSIA ( absolute pressure) is PSIG from your gauges plus atmospheric pressure. In this area, we would use 14.7 added to our gauge reading.
    Hope this helps!

  4. Likes stanbyyourword liked this post
  5. #4
    Join Date
    Sep 2002
    Location
    South Dakota
    Posts
    6,580
    Post Likes
    The most useful application of compression ratio on cascade systems is when you are designing one and you need to know how many cascade stages it will take to divide up the total compression ratio. And, to determine how much of the total ratio each stage will take.


  6. #5
    Join Date
    Jun 2001
    Location
    Michigan
    Posts
    12,077
    Post Likes
    I would like to know how to do this.

    Disharge pressure is 230 psi + 14.7 = 244.7 psi Total DP

    Suction pressure is 37 psi + 14.7 = 51.7 psi Total SP

    244.7 total discharge pressure divided by 51.7

    244.7/51.7 = 4. So it has a 4 to 1 compression ratio.

    Am I even close to being correct??


  7. Likes syndicated, Fathma liked this post
  8. #6
    Join Date
    Feb 2004
    Location
    Medford Oregon
    Posts
    807
    Post Likes
    Dowadudda

    Yes, you got it right
    the next step would be to compare against
    compressor curve (available from Cpeland distr)

  9. Likes Cherryair liked this post
  10. #7
    Join Date
    Sep 2002
    Location
    South Dakota
    Posts
    6,580
    Post Likes
    You get far more useful information if you obtain your saturated suction temperature and pressure and your saturated discharge temperature and pressure. Then obtain a capacity chart for your particular compressor and then you can read the following off the chart.

    1. Actual compressor capacity in btuh for those conditions
    2. Actual total heat of rejection out the compressor discharge and into the condenser
    3. Actual operating wattage for those conditions

    Using the chart you can move around on the chart and see exactly what the results will be if you change the high side or low side pressure. You can see how many btuh of compressor capacity you will gain or loose with different suction and discharge pressures.

    This is far, far more useful than messing with compression ratio. I have used both and compared them to each other. Small changes in compression ratio actually amount to great changes in compressor capacity and power consumption. Compression ratio is just not accurate enough to be meaningful compared to the compressor charts.



  11. #8
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    13,074
    Post Likes

    Compressor Data.......

    The hardcopy compressor performance data is a thing of the past. Go to Copeland's website: http://www.copeland-corp.com/ and download their Compressor Performance Calculator program. (You'll have to register first if you're not already in the system)

    I've got it on my laptop in the truck. I can print out a performance sheet with all the data I need.......pretty cool.

    [Edited by icemeister on 07-19-2004 at 05:43 PM]

  12. #9
    Join Date
    Sep 2013
    Posts
    6
    Post Likes
    Where did you find the compress performance calculator

  13. #10
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    13,074
    Post Likes
    Quote Originally Posted by Rodney2476 View Post
    Where did you find the compress performance calculator
    Things have changed a bit since 2004, but the software is still available:
    https://opi.emersonclimate.com/was.e...?action=xtools

    Look for the Product Selection Software.

  14. #11
    Join Date
    Sep 2013
    Posts
    6
    Post Likes
    Thank you sir appreciate the help

  15. #12
    Join Date
    Sep 2013
    Posts
    6
    Post Likes
    I had to download the software. Not sure if I'm looking at what you have

  16. #13
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    4,099
    Post Likes
    Knowing how the CR works is just another Troubleshooting tool. Small, rarely used,not known much about,CR. After changing out a comp I always look at the CR, its just a few steps in the brain. In AC, CR just doesn't have that much of a "big deal" affect to it. Now on R -med,lo,xlo temps it seem that CR is more important. And the bad/rotten CR of freezers IS a comp killer, if allowed to run under those"wrong conditions". Copeland makes a Scroll for low temp , that operates in a normal "high CR conditions" all the time. So,that means that CR is much more critical in the "R" trade,I think.

    AS A NOTE: I recently bought and read a book by NormChris in above posts. Its called "Airside System Analysis" by Norm Christopherson. It shows examples and explanations of "stuff" that I see,and run across, so it means something to me. Norm uses the Psychrometric Chart, but "not to worry" here. He made me see more! Its a Good Read!

  17. Likes Cherryair liked this post