Results 1 to 6 of 6
  1. #1
    Join Date
    Jul 2004
    Location
    West TN
    Posts
    986
    Post Likes
    Arghhh don't ya just hate when this happens.

    Was working on an AC unit at a Huddle House.
    Checked the unit from head to toe and couldnt' find anything wrong with it.
    Pressures, superheat, subcool, amperages, CFM.... everything... right on the money.
    But why for it not cool?

    The dad blame fresh air for the vent a hood.
    Arghhh

    It wasn't adding enough fresh air for the hood and made the building go into a vacuum pulling in hot air from every nook and cranny.
    Nice breeze coming in the door when ya crack it.




  2. #2
    Join Date
    Feb 2002
    Posts
    211
    Post Likes
    good find.

    The kitchen hood exhaust might be pulling too much also.
    but unless you can verify your maintaining minimum required fpm in exhaust duct you may cause a fire hazard by slowing it down.

  3. #3
    Join Date
    May 2004
    Posts
    13,019
    Post Likes
    Good point Islander.


    Also check to see if the RTU’s have minimum outside air dampers. Usually set to 20%.

    My rule of thumb may not be right for you but here it is

    100 CFM of outside air x # of A/C tons = good exhaust make up

    (*if the exhaust fans are properly sized and there is NOT a make up air hood)

    Use the ol’Napkin test. Open the rear door and see if a limp napkin pulls in or blows out.

    Out = Positive
    In = Negative

    Much rather be a POSITIVE person than a grumpy ol’ man.


  4. #4
    Join Date
    Sep 2002
    Posts
    186
    Post Likes
    Is there a make-up air unit? Almost all kitchen hood I have worked on have air blowing in on the frontside and exhaust on the backside. Look on the roof for that make-up air fan maybe plugged filters.
    Because chicks dig it.

  5. #5
    Join Date
    Jun 2004
    Location
    Richmond Virginia
    Posts
    1,078
    Post Likes
    I cut my teeth on restaurant work; even the food service equipment. I still can't open the door of a restaurant without my face by the door to feel if the building is on a positive or negative. Most (especially the older they get are on a negative). Also can't drink my drink without first determining what brand icemaker made the ice. I'm a sick man.

  6. #6
    Join Date
    Feb 2001
    Posts
    35,838
    Post Likes

    Talking

    That and the A/C unit is marginally sized......to say the least.
    Hey cockroach, don't bug me! ©

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.