Page 3 of 3 FirstFirst 123
Results 27 to 28 of 28
  1. #27
    Join Date
    Aug 2004
    Location
    Kansas
    Posts
    133
    Post Likes

    oil safety

    Thanks Rocket
    For an update for me that a Copeland Engr states 5 psi on the crankcase check valve instead of 1/2 psi. Can you help me with the same psi information on a Carlyle? Why is the check valve there? Is it to flash off the liquid refrigerant out of the oil or prevent the oil from backing up out of the crankcase into the motor cavity?

    I'm still learning at 55

  2. #28
    Join Date
    Jun 2004
    Posts
    182
    Post Likes
    therock, rocket,

    I started a new post on checking for a pressurized crankcase. The oil check valve is not spring loaded and the 5psi differtial is incorrect also. Please refer to pressurized crankcase for more.

    Thanks basser

Page 3 of 3 FirstFirst 123

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.
Comfortech 365