    I have a code that is "Bad Volts sen" this is word for word
    This unit does not have any device that senses voltage drop
    All 3 legs have 480-495 volt well with in the 10% drop.
    Any ideas. It is locked out and wouldn't reset.

  2. #2
    Join Date
    Mar 2003
    Posts
    1,877
    Post Likes
    get the manual for that chiller and find out what it means.

  3. #3
    Join Date
    Jul 2004
    Posts
    2
    Post Likes
    Is this a micro tech 200 i was a field tech for them and had the same problem. If its a micro tech 100 then check the current tranformer

  4. #4
    Join Date
    Apr 2004
    Posts
    423
    Post Likes

    you probly have a bad sensor

    what is the modle number?

  5. #5
    Join Date
    May 2002
    Posts
    43
    Post Likes
    Temporarily jumper the phase monitor control circuit and see if you can clear the alarm. If it does, check setting on the monitor to verify that it agrees with the actual voltage. If you still have a problem, the control contact on the monitor may be suspect.............. several monitors were used, so, I can't be specific regarding the monitor.

  6. #6
    Join Date
    Aug 2002
    Posts
    37
    Post Likes
    Thread Starter
    its a alr35d and the manual says nothing.

  7. #7
    Join Date
    Jun 2002
    Posts
    48
    Post Likes
    Where's chillermech when do need him? You're probably having a intermittent bad connection on the MCB board. Clean terminals and re-seat wires in connector.


  8. #8
    Join Date
    Feb 2002
    Location
    Toronto
    Posts
    194
    Post Likes
    Its telling you there is a problem with the regulated power supply to the transducers. Theres a test procedure in the IM under troubleshooting power problems

  9. #9
    Join Date
    May 2002
    Posts
    43
    Post Likes
    Hey SalesSlime, I believe this is confusing due to the statement..... bad volts ratio is the one you're thinking about. I'm pretty sure the statement is an earlier version of phase/volts

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •