Results 14 to 18 of 18
Thread: Trane RTA
    Oregon
    Thats pretty good because it is a shell and coil evaporator, not shell and tube.
    Michigan
    Hey guys got it fixed
    Sorry to report I jumped waaaayyyyy ahead of myself.
    It is a 200 ton RTAC.
    Had to pull the building down, damn triple duties, and pull the strainers. Yup 3/4 plugged. Measured a 10 # differential after they were cleaned and a 5 # across the barrel. All is well. Lesson learned - PM is very important.
    Thanks ALL.
    Not in Iran
    Confused
    Quote Originally Posted by durussel78 View Post
    Hey all
    have a trane RTA Chiller - twin screw. CKT 1 is tripping on low evap temp.
    CKT 2 runs all day but is only pumping out 50 deg water - by the time it is reaching the secondary it is 58 deg. Could this be a plugged strainer on the primary if so why is the secondary so warm and why is this thing running if it is plugged. thanks guys
    if ckt 2 runs all day, but ckt1 trips on low evap why and how is this?
    is this because ckt 2 is at 100% and ckt 1 energized to meet setpoint..
    a plugged evap water flow strainer will cause this.,? why would it not trip both ckt 1 & 2?
    no signature blast'em man blast'em
    !!!KILL THE TERRORIST!!!
    DFW
    Because he is loosing the building load. He stated 50 degree water. Which means even with low flow he is above trip points. When all circuits are running and pulling the temp down to setpoint or lower the compressor/s cannot unload quick enough. It may depend on which compressor is started first. I have seen low evap alarms and low ref temp alarms due to water flow. It all depends on the rla of the compressors at the time of low water flow. Such as primary variable water systems.
    Quote Originally Posted by mlkwal1 View Post
    he never did give us any performance numbers to work with. it is possible that circuit #2 has other issues or is riding the edge of tripping but it just isn't tripping...yet. small differences can make big differences...if you get my meaning.