    Can anyone tell me the approximate CFM of a Westinghouse air handler A001600W1, style 353A447G11? I'm hoping someone has an old catalog or has worked with Westinghouse equipment in the past.

    Thanks.

    Jim.

  2. #2
    Join Date
    May 2004
    Posts
    125
    iTS BEEN A WHILE SINCE I SEEN ONE BUT I THOUGHT THE 1600( IN THIS CASE)IN THE M# WAS THE CFM. COULD IT BE A FOUR TON UNIT??????

  3. #3
    Join Date
    Jul 2004
    Posts
    33
    Yep, that was pretty much what I thought, but the supply air ductwork is 24/14 which at 0.1"/100' static rate is 2500 CFM. 1600 CFM at that duct size is 0.04"/100', a pretty conservative duct size, to say the least.

    They ran a very long refrigerant line, 5/8 liquid line (good for 5-25 tons) and a 1 1/8 suction line (good for 2.5-13 tons) so the 4-tons is reasonable from that standpoint.

    I'm trying to replace an existing air handler, and I'd like to replace it like-for-like, since it works now.

    Did I meantion this is a rare book library???

    Thanks.