Walk in freezer
Only 1 of the 2 evap fan motors is running.
Are there any devices that would only control 1 of the fan motors?
-
07-09-2004, 12:39 PM #2
nope
Bad motor or bad wiring.
Experience is what you have an hour after you need it.
-
07-09-2004, 02:20 PM #3
Professional Member*
- Join Date
- Nov 2001
- Location
- East Texas
- Posts
- 832
Nevermind, the motor was toast. It was a 115v, shoulda been 208/230v.
Its freezing in that sucker now. -10.
-
07-09-2004, 05:49 PM #4
Just for future reference.
There may be a fan cycle control operating one fan motor. If you do see this, change the wiring to cycle both fans.
There also may be an ambient sensor mounted above or near the fans. The ambient sensors are junk (in my opinion) and should be cut out and a fan cycle control installed.
If there is a headmaster in the refrigeration circuit and a fan cycle control then the headmaster is probably bad and wasn't taken out.
If you can, remove the headmaster and use the fan cycle. If you can't remove it then pinch off the by-pass line. Watch your flow pattern and don't pinch off the wrong liquid line. Please don't just pop the nitrogen fill port tube, some of them will leak refrigerant through the tube.
Just for reference on other jobs.