    what do you think happened???

    Went on a call today and saw 2 compressors blown out at electrical pins, 2 contactors welded shut, all wires burnt, oil all over the door from the compressors, but the fuses did not open up.
    Trane m= TTA150B300FA s= 8161P4PAD.
    This is a split system with the evap coil 24 feet above the condensor, no traps in the suction line but there is a pig tail trap in both liquid lines. I dont have a good diagnosis to tell the customer yet except the obvious.

  2. #2
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    70,520
    Post Likes
    System had a leak, compressors went into a vacuum, electrical arcs in the compressor burned out the terminals, air entered the holes where the terminals burned out, overheated oil vapor in compressors ignited from the electrical arcing and blew the fusetite plugs out spewing burnt refrigerant oil all over the place.

    Bummer.
    Training is important!
    Practical Training is a must!

  3. #3
    Join Date
    Oct 2003
    Location
    34.8n 102.4w
    Posts
    3,241
    Post Likes
    Very good diagnosis there Robo.....May cut and paste that on a few invoices...
    Life goes on long after the thrill of living is gone.

  4. #4
    Join Date
    Feb 2007
    Location
    michigan
    Posts
    71
    Post Likes
    Thread Starter
    Robo, I take it you've seen this before. Also that make sense since the 1st and 2nd stage were tied together. Why??? I have no idea (LOW BID) I guess.
    I'm going to check with Trane but do you think they need A trap on the lines.

  5. #5
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Quote Originally Posted by RoBoTeq View Post
    System had a leak, compressors went into a vacuum, electrical arcs in the compressor burned out the terminals, air entered the holes where the terminals burned out, overheated oil vapor in compressors ignited from the electrical arcing and blew the fusetite plugs out spewing burnt refrigerant oil all over the place.

    Bummer.
    That's a great explanation, sir.

    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  6. #6
    Join Date
    Apr 2006
    Location
    mechanical room
    Posts
    1,790
    Post Likes
    just a inverted trap at the ahu, and make sure you put a liq. line solenoid valve in

  7. #7
    Join Date
    Jan 2010
    Posts
    45,370
    Post Likes
    [QUOTE=toptwo;6781142] Also that make sense since the 1st and 2nd stage were tied together.

    Because they only had a single stage thermostat.

  8. #8
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    70,520
    Post Likes
    Quote Originally Posted by toptwo View Post
    Robo, I take it you've seen this before. Also that make sense since the 1st and 2nd stage were tied together. Why??? I have no idea (LOW BID) I guess.
    I'm going to check with Trane but do you think they need A trap on the lines.
    I have indeed run across a few of these. I have also had the unpleasant experience of having one blow while I was standing next to the unit. A change of underwear was in order that day. A very loud "BANG" followed by plumes of obnoxious smelling oily vapor is not a thing that will make your day.
    Training is important!
    Practical Training is a must!

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •