    If I see one more trap with the vent tee on the unit side of the trap instead of downstream of the trap I'm gonna lose it!. How tough can it be to get a trap right???. seems like 3 out of 4 I run into are piped wrong. just random chance should make it fifty/fifty. just venting folks, as you were.
    How can you have any pudding if you don't eat your meat?

  2. #2
    Join Date
    May 2002
    Location
    Colorado
    Posts
    697
    Post Likes
    Some may want a vent on the equipment side so you can pour in bleach to clear the trap and the drain line. So the best solution is two vent tees. But put a removable cap on the equipment side. And make sure the downstream vent opening is higher than the upstream line!

  3. #3
    Join Date
    Jul 2001
    Location
    Central MN and the Twin Cities
    Posts
    1,541
    Post Likes
    That is common in residential around here. The capped vent before the trap is great for filling them when they are dry in the spring after they dry out in the winter.
    Warning: Just because I am over the head injury doesn't mean I'm normal!

    The day I stop learning.... I'm dead!

  4. #4
    Join Date
    Jan 2004
    Location
    New Jersey
    Posts
    534
    Post Likes

    > Condensate Traps!

    Originally posted by ozone drone
    If I see one more trap with the vent tee on the unit side of the trap instead of downstream of the trap I'm gonna lose it!. How tough can it be to get a trap right???. seems like 3 out of 4 I run into are piped wrong. just random chance should make it fifty/fifty. just venting folks, as you were.







    Nice venting about Vents!!!

  5. #5
    Join Date
    Mar 2002
    Location
    Richmond, Virginia
    Posts
    4,264
    Post Likes
    I always install a bullheaded tee as close to the coil outlet as possible and connect a 'p' trap to the bottom of the tee. This way I can look into the trap and can clean it out. I then plug the tee with a short piece of pvc with a cap glued to the top of it. I've seen many done this way without a cap however. Some use those rubber plugs from compressor suction lines or tape them shut and later these things get lost. I agree however that the tee should NOT be left open.
    There is nothing more frightful than ignorance in action....Mark Twain

  6. #6
    Join Date
    May 2001
    Location
    Bennington, Vermont U.S.A.
    Posts
    13,856
    Post Likes
    My son and I always argue about traps and condensate lines. He is completely convinced that he can defy the laws of gravity.

  7. #7
    Join Date
    May 2004
    Location
    Rapid City, SD
    Posts
    7,416
    Post Likes
    We got a flyer for the "proper" way to vent condensate lines not too long ago. This was after several plumbers and installers were doing them backwards. I do like the idea of putting a T before the trap (capped) so you can fill it up and clean it out easier.

  8. #8
    Join Date
    Oct 2003
    Posts
    566
    Post Likes
    I have witnessed water running uphill
    Hey mosquito, quit biting (slap!!) me...
    Anyone like Josey Wales?
    C'mon, you know I'm right!

  9. #9
    Join Date
    Jan 2003
    Location
    Beaufort, SC
    Posts
    2,821
    Post Likes
    We don't use tee's, they are useless, bleach doesn't do a whole lot, we just hook a good wet vac outside and let her rip, cleans it all. 98% of what we do is heat pumps.

  10. #10
    Join Date
    Apr 2002
    Location
    Dallas TX
    Posts
    2,217
    Post Likes
    We use traps and T'son every primary drain. If it is a positive pressure coil we put the vent between the unit and the trap so we can elminate the glug effect you may see. On negative pressure it is for access to blow the line with certain adapters. If you put them in backwards though they obviously do not work very well.

  11. #11
    Join Date
    Jul 2001
    Location
    Central MN and the Twin Cities
    Posts
    1,541
    Post Likes
    Originally posted by hvac45
    We don't use tee's, they are useless, bleach doesn't do a whole lot, we just hook a good wet vac outside and let her rip, cleans it all. 98% of what we do is heat pumps.
    Yep just add that to the list of differences between the south with heatpumps and the north with furnace/ac's. We have to put an access in.(T with cap) The ac will be off for over 6 months and the traps dry out in the fall/winter. We need to fill them with the spring clean and check or "no good." Learned your vac trick from a guy in Sarasota, FL over 10 yrs ago. Still hasn't really caught on around here!?! Go figure.
    Warning: Just because I am over the head injury doesn't mean I'm normal!

    The day I stop learning.... I'm dead!

  12. #12
    Join Date
    Mar 2002
    Location
    Richmond, Virginia
    Posts
    4,264
    Post Likes
    Originally posted by grasshopper
    Originally posted by hvac45
    We don't use tee's, they are useless, bleach doesn't do a whole lot, we just hook a good wet vac outside and let her rip, cleans it all. 98% of what we do is heat pumps.
    Yep just add that to the list of differences between the south with heatpumps and the north with furnace/ac's. We have to put an access in.(T with cap) The ac will be off for over 6 months and the traps dry out in the fall/winter. We need to fill them with the spring clean and check or "no good." Learned your vac trick from a guy in Sarasota, FL over 10 yrs ago. Still hasn't really caught on around here!?! Go figure.
    Hey wait! I'm in the south and do primarily heat pump work and I use the tees. Pull the capped stem out of it and slide a special rubber adapter that I made up which seals me from the coil outlet and hit it with a swoosh cartridge and all done! I bought one of the $99.00 Dewalt wet vacs that uses any of their battery pacs and also runs off of 120 volts also. That thing is sweet. Just vacuumed two lines from outside with it yesterday.
    There is nothing more frightful than ignorance in action....Mark Twain

  13. #13
    Join Date
    Jan 2003
    Location
    Beaufort, SC
    Posts
    2,821
    Post Likes
    Bought the dewalt a couple a months ago, your right its great, especially for emergency pans in the attic, and the side drain works nice, a p-trap fits perfect in the end for the drains that come out to close to the ground with a 90 on them.