    hi, should evap run at about 5 degrees

  2. #2
    Join Date
    Feb 2001
    Posts
    35,838
    Post Likes
    I think you need to post this one more time in every section, just in case somebody missed it
    Hey cockroach, don't bug me!

    www.AskTheDiceman.com

    www.TheColdConspiracy.com

    www.Pennwood-HVAC.Com

    Bring Em Home....

  3. #3
    Join Date
    Mar 2003
    Posts
    1,877
    Post Likes
    saturated suction temperture should be 15 to 20 degrees below box temperture setpoint.
    if you have a box that is to maintain 35 degrees lets say r12 then suction pressure should be 17 to 21 lbs.which would correlate to an evap temp of 15 to 20 degrees.

  4. #4
    Join Date
    Jun 2004
    Posts
    55
    Post Likes

    Wink not sure

    thanks airworx