hi, should evap run at about 5 degrees
-
06-27-2004, 11:31 AM #2
I think you need to post this one more time in every section, just in case somebody missed it
Hey cockroach, don't bug me! ©
www.AskTheDiceman.com
www.TheColdConspiracy.com
www.Pennwood-HVAC.Com
Bring Em Home....
-
06-27-2004, 07:23 PM #3
Member
- Join Date
- Mar 2003
- Posts
- 1,877
saturated suction temperture should be 15 to 20 degrees below box temperture setpoint.
if you have a box that is to maintain 35 degrees lets say r12 then suction pressure should be 17 to 21 lbs.which would correlate to an evap temp of 15 to 20 degrees.
-
06-28-2004, 05:26 PM #4
Regular Guest
- Join Date
- Jun 2004
- Posts
- 55
not sure
thanks airworx