05-15-2010, 02:44 PM #1
absorber a** kicking
I have a York M/N YIASTIA2. Its a little machine, however I cannot get it to make range, stop crystallizing, and I never see any evap overflow. It takes FOREVER to load up. Once it loads and makes temp, it backs off and goes into ADC mode. My refrigerant is trashy. I feel overflow as soon as my steam valve opens. I have a clean bill of health from the chemist, I added a half gallon of alcohol, and I have a great vacuum. My flows are in range, and the "engineers" punched the tubes. Here are the numbers:
Steam: 14.39psia after the valve, 21psia feeding the valve, 230F outlet. Valve at 82% (machine loading)
Refrigerant: 62F, S.G. 1.12,
Chilled Water: 64F on, 58 off.
Condenser: ABS in 81, 87 out, 93 cond out.
Weak Solution: 97F, S.G. 1.56, 121F to generator.
Strong Solution: 178F into the HX, 120F out. 1.64 S.G
The rate limit is set to .5, and the valve pulse is set to 1 minute.
My main concern is a huge (80f) TD between the strong solution into the HX and the strong solution leaving the HX, I have de-crystallized the machine, but nothing changes.
I need help!
-
05-15-2010, 03:55 PM #2
Professional Member*
- Join Date
- Jan 2009
- Location
- Jersey
- Posts
- 119
what is the pressure of the absorber section,
what is the chilled water setpoint.
and what is the purge bubble rate?
-
05-15-2010, 05:06 PM #3
I ain't no expert but mabey these IOM's could help you out to figure out your problem they have helped me out tremendously in the past good luck.
Arguing with your Boss is like wrestling with a pig in
mud.
After a while you realize that while you are getting
dirty, the pig is actually enjoying it.
It is not exactly cheating, I prefer to consider it
creative problem solving.
-
05-15-2010, 05:54 PM #4
York56, thank you very much for the books!
DFZ, the absorber pressure is 7-8 mils, the bubble rate is imperceptible, and the chilled water set point is 45.
-
05-15-2010, 07:15 PM #5
Professional Member
- Join Date
- Aug 2000
- Location
- USA
- Posts
- 4,933
Clean your refrigerant up. At 62F with 1.12sg you have about a 15% concentration of solution in your refrigerant. Should be close to 0% solution in your refrigerant. Cut your steam regulater back. Should be around 10PSI at the generater inlet at full load. Relog and post.
Your poor planning does not constitute an emergency on my part!!!!
-
05-16-2010, 08:59 AM #6
Professional Member*
- Join Date
- Jan 2009
- Location
- Jersey
- Posts
- 119
absorber section should be about 6mm
as you clean up the refrigerant the pressure may drop on its own
it does look to be fouled refrigerant.
hope all of this is helpfull.
-
05-16-2010, 09:14 AM #7
Thanks for the help. How do I clean up my refrigerant? My steam is already 3-4 psig below design.
If I increase the pressure, will I increase the rate of distillation, or will I over concentrate the machine?
-
05-16-2010, 09:47 AM #8
Professional Member
- Join Date
- Aug 2000
- Location
- USA
- Posts
- 4,933
Should be a (hand) dump valve on the discharge line of the refrigerant pump that goes into the solution side. Just open it up. It may be 2sol on your machine on page 26 and you may not have a hand valve. Ooops, I see your steam is in PSIA not PSIG. Probably have to log into service mode and go in with 1380 to manually open the dump valve.
"These solenoid Valves can
be manually controlled only when “Manual Solenoid
Control” is selected. Instructions for selecting the desired
control mode are contained in the IsoFlow Control Center
“Service” manual, Form 155.16-M3 in “Special Programming
Procedures” section."Last edited by absrbrtek; 05-16-2010 at 10:05 AM.
Your poor planning does not constitute an emergency on my part!!!!
-
05-16-2010, 12:26 PM #9
thank you much, absrb! I wired a bypass switch in for 2sol on friday when i tried to decystalize the machine. I guess i didn't leave it on long enough, I was afraid to starve the refrigerant pump. I give it another go on monday, and let you all know how it goes.
thanks again!
-
05-19-2010, 07:35 PM #10
Professional Member
- Join Date
- Aug 2000
- Location
- USA
- Posts
- 4,933
-
05-19-2010, 09:33 PM #11
It has been cool here on the east coast the week, and the customer has been relying on other means to cool this building. I hope to get out there Friday as we should be having a nice warm day. I will be sure to give a proper update.
Thank you all again for your help!
-
05-20-2010, 10:31 PM #12
If the machine has a history of leaks, you've got a tiger by the tail.
I inherited a sick Trane unishell and fought with it for a while, a few years back.
It had a history of leaks, and you couldn't even see through the sight glass.
When we scrapped it the solution heat exchanger was so full of crud that it was a wonder it worked at all. Stack up city.
Abs. is probably the best guy around here on absorbers.
Listen and learn. He da man.God Bless the USA
-
05-25-2010, 08:46 AM #13
Professional Member
- Join Date
- May 2010
- Location
- Springfield, MO
- Posts
- 40
Carrier 16JB Absorption Chiller Crystallization
I'm currently fighting a crystallization on a single effect, steam fired 450 ton Carrier 16JB. I'm almost positive it's crystallizing in the lower solution heat exchanger, but I'm running out of ideas and can't get my water below 54 degrees. Any ideas, tricks or suggestions would be much appreciated.